    Estimating server power usage

    I am trying to estimate power usage for the purpose of looking for colocation offers and am wondering what you guys think the draw for this server would be. Thank you for all your help.

    ​4U Supermicro X7DB8 motherboard
    Dual Quad-Core Xeon E5345 2.33GHz
    8GB DDR2 PC-5300 RAM
    Adaptec AID-9140w SAS/SATA Controller
    6x Hitachi 36GB 15k rpm Hard Drives in RAID 10
    2x Western Digital 250GB Hard Drives for backup
    Last edited by jjtoday; 11-10-2009 at 11:35 PM. Reason: Title spelling fix

  2. #2
    Join Date
    Apr 2009
    Location
    Dallas/FortWorth TX
    Posts
    1,677
    i would assume this config should draw around 6 amps more or less.
    IPStrada When uptime counts.
    Warren Buffet: Honesty is very expensive gift do not expect it from cheap people.

  3. #3
    Join Date
    Nov 2009
    Location
    Reston
    Posts
    305
    Quote Originally Posted by jjtoday View Post
    I am trying to estimate power usage for the purpose of looking for colocation offers and am wondering what you guys think the draw for this server would be. Thank you for all your help.

    ​4U Supermicro X7DB8 motherboard
    Dual Quad-Core Xeon E5345 2.33GHz
    8GB DDR2 PC-5300 RAM
    Adaptec AID-9140w SAS/SATA Controller
    6x Hitachi 36GB 15k rpm Hard Drives in RAID 10
    2x Western Digital 250GB Hard Drives for backup
    If you have the server already, the easiest way to get the power draw is to plug it into a kill-a-watt meter... They are cheap to buy... But keep in mind power draws are going to vary depending on CPU usage and cooling factors (fans will run more etc).... It's impossible to really say how much this server is going to draw if you need an exact number.

  4. #4
    Join Date
    Feb 2004
    Location
    Phoenix, AZ
    Posts
    162
    The easiest way to get a wattage figure is to go by the power supply rating. That gives a peak consumed power estimate, though it should be higher than the actual watts used. If the server uses a 1200W PS, then it needs at most 10 Amps at 120V. At least in theory.
    bigwrench

  5. #5
    Join Date
    Dec 2001
    Location
    Toronto, Ontario, Canada
    Posts
    5,954
    I'd put my money between 2.25A and 3.75A @ 110/120v (depending on PSU efficiency, number of dimms, and type of dimms, and quantity/type of fans)

    The E5345 has a TDP of 80W, hence a 6.0A estimate @ 120V is wayyyy out in left field.

  6. #6
    Join Date
    Apr 2009
    Location
    Dallas/FortWorth TX
    Posts
    1,677
    Quote Originally Posted by porcupine View Post
    I'd put my money between 2.25A and 3.75A @ 110/120v (depending on PSU efficiency, number of dimms, and type of dimms, and quantity/type of fans)

    The E5345 has a TDP of 80W, hence a 6.0A estimate @ 120V is wayyyy out in left field.
    True, CPU's dont consume much power, but we are talking about 8 HDD here.
    IPStrada When uptime counts.
    Warren Buffet: Honesty is very expensive gift do not expect it from cheap people.

  7. #7
    Join Date
    Dec 2001
    Location
    Toronto, Ontario, Canada
    Posts
    5,954

  8. #8
    Join Date
    Aug 2006
    Location
    Ashburn VA, San Diego CA
    Posts
    4,571
    Quote Originally Posted by porcupine View Post
    I'd put my money between 2.25A and 3.75A @ 110/120v (depending on PSU efficiency, number of dimms, and type of dimms, and quantity/type of fans)

    The E5345 has a TDP of 80W, hence a 6.0A estimate @ 120V is wayyyy out in left field.
    Sounds about right. I'd say ~3A.
    Fast Serv Networks, LLC | AS29889 | Fully Managed Cloud, Streaming, Dedicated Servers, Colo by-the-U
    Since 2003 - Ashburn VA + San Diego CA Datacenters

  9. #9
    Join Date
    Oct 2009
    Posts
    58
    Quote Originally Posted by IPStrada LLC View Post
    i would assume this config should draw around 6 amps more or less.
    yes I agree with you dude! thanks

  10. #10
    Join Date
    Jan 2003
    Location
    Chicago, IL
    Posts
    6,889
    Quote Originally Posted by porcupine View Post
    I'd put my money between 2.25A and 3.75A @ 110/120v (depending on PSU efficiency, number of dimms, and type of dimms, and quantity/type of fans)

    The E5345 has a TDP of 80W, hence a 6.0A estimate @ 120V is wayyyy out in left field.
    I would agree with your estimate.

    160w for the CPUs, 120w for the drives, 110w for the motherboard, fans and other components. With an ~85% efficient power supply you're right at the top end of that, 3.7A at 120v and the numbers I provided are peak numbers, so you should pretty much always run less than those.
    Last edited by KarlZimmer; 11-12-2009 at 03:58 PM.
    Karl Zimmerman - Steadfast: Managed Dedicated Servers and Premium Colocation
    karl @ steadfast.net - Sales/Support: 312-602-2689
    Cloud Hosting, Managed Dedicated Servers, Chicago Colocation, and New Jersey Colocation
    Now Open in New Jersey! - Contact us for New Jersey colocation or dedicated servers

  11. #11
    Join Date
    Sep 2008
    Location
    Dallas, TX
    Posts
    4,552
    Quote Originally Posted by porcupine View Post
    I'd put my money between 2.25A and 3.75A @ 110/120v (depending on PSU efficiency, number of dimms, and type of dimms, and quantity/type of fans)

    The E5345 has a TDP of 80W, hence a 6.0A estimate @ 120V is wayyyy out in left field.



    I'd say probably 3 or 4 amps just because of the large number of hard drives.
    Jacob Wall - GetCloak.com

  12. #12
    Join Date
    Oct 2009
    Posts
    58
    Quote Originally Posted by Jacob Wall View Post



    I'd say probably 3 or 4 amps just because of the large number of hard drives.
    Yeah 3-4 AMPS is also my guess.. As he said it has a large number of hard drives.

  13. #13
    Thank you all for your estimates. Until I get a measurement, I will use a 4A estimate to be a little bit on the safe side.

  14. #14
    Join Date
    Mar 2009
    Posts
    2,218
    Quote Originally Posted by bigwrench View Post
    The easiest way to get a wattage figure is to go by the power supply rating. That gives a peak consumed power estimate, though it should be higher than the actual watts used. If the server uses a 1200W PS, then it needs at most 10 Amps at 120V. At least in theory.
    Server manufacturers only have a limited range of power supplies.

    For each model of server, the use the next-higher power supply that is capable of powering a maximally configured server running flat out in a room whose temperature is the highest the server can run in (so the fans are running hardest.)

    In practice, you may find the server is using about half the power that the power supply can deliver.

  15. #15
    Join Date
    Jun 2003
    Location
    London, UK
    Posts
    1,733
    We have dual quad core, 8 SAS disk machines drawing 1.5A @ 220V (Dell R710), so I'd estimate this machine to use ~3.5A @ 110V.
    Darren Lingham - UK Webhosting Ltd. - (0800) 024 2931
    Tsohost.co.uk - Quality UK Windows and Linux hosting since 2003
    UK WordPress Hosting - Fast, easy, cloud based WordPress Hosting

  16. #16
    Join Date
    Feb 2004
    Location
    Phoenix, AZ
    Posts
    162
    Quote Originally Posted by tim2718281 View Post
    In practice, you may find the server is using about half the power that the power supply can deliver.
    I agree and it's done to handle normal current surges like spinning up all drives at poweron, peak cpu bursts on all cores, and don't forget a PS also powers any optional add-on cards and external devices (USB, firewire, etc). PS wattage is a rough estimate, but it's an estimate!
    bigwrench

  17. #17
    Join Date
    Dec 2001
    Location
    Toronto, Ontario, Canada
    Posts
    5,954

Similar Threads

  1. Estimating email load on a server
    By bjseiler in forum Programming Discussion
    Replies: 11
    Last Post: 01-17-2003, 06:08 PM
  2. Estimating server needs based on traffic
    By leftofcentre in forum Dedicated Server
    Replies: 7
    Last Post: 12-16-2002, 05:48 PM
  3. Estimating Bandwith
    By ginagamo in forum Web Hosting
    Replies: 7
    Last Post: 08-10-2002, 11:34 PM
  4. Estimating Speed
    By NVB in forum Web Hosting
    Replies: 0
    Last Post: 08-06-2001, 12:43 PM
  5. Estimating traffic...
    By Badger_Hoss in forum Web Hosting
    Replies: 1
    Last Post: 07-26-2001, 06:30 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •