  1. #1

    Does anyone exceed 80% on primary/redundant circuits?

    So the rule of thumb is if you have a 30A circuit to not exceed 80% or 24A.

    If I buy a 30A circuit, I am assuming it is protected by a circuit breaker that is 30A, correct?

    In *theory* we could run 29-30A all day and be fine.

    So, I understand, the rule of 80% to be to the effect that "during startup, equipment uses more power ... or during runtime if it heats up, the fans go faster using more power" so it is safe to be at 24A in case you get spikes to 27-29A.

    Is my reasoning correct?

    Further, if you run primary/redundant circuits, is there really harm in running 13A on one circuit and 14A on the other.. and in the unlikely event of a failure, you are running 27A on one circuit (at 90% instead of 80%).

    Any thoughts on this? Getting an extra 3A out of a 208V circuits is like putting in 3-4 more servers. If someone is doing this please let me know. I think it would work fine but i would like to know from the experts that do the colo stuff for a living what problems i could encounter, if any.

  2. #2
    Join Date
    Dec 2007
    Location
    Isle of Man
    Posts
    3,068
    It is POSSIBLE however there is a VERY HIGH potential of the circuit breaking if over 80% is consumed.

  3. #3
    Join Date
    Sep 2004
    Location
    San Jose
    Posts
    66
    Quote Originally Posted by shunter1 View Post
    So the rule of thumb is if you have a 30A circuit to not exceed 80% or 24A.

    If I buy a 30A circuit, I am assuming it is protected by a circuit breaker that is 30A, correct?

    In *theory* we could run 29-30A all day and be fine.

    So, I understand, the rule of 80% to be to the effect that "during startup, equipment uses more power ... or during runtime if it heats up, the fans go faster using more power" so it is safe to be at 24A in case you get spikes to 27-29A.

    Is my reasoning correct?

    Further, if you run primary/redundant circuits, is there really harm in running 13A on one circuit and 14A on the other.. and in the unlikely event of a failure, you are running 27A on one circuit (at 90% instead of 80%).

    Any thoughts on this? Getting an extra 3A out of a 208V circuits is like putting in 3-4 more servers. If someone is doing this please let me know. I think it would work fine but i would like to know from the experts that do the colo stuff for a living what problems i could encounter, if any.

    The National Electrical Code says you can not exceed 80% of a breakers rating for continuous loads. Computers are continuous load per the NEC. If you exceed 80% you are violating the NEC, local fire code, and likely your contract with your colo company. And on top of that, your circuit is at risk for tripping.
    Steve Rubin - ser@layer42.net
    Layer42 Networks - http://www.Layer42.net/

  4. #4
    Join Date
    Sep 2008
    Location
    Dallas, TX
    Posts
    4,568
    I've seen people run a 20A circuit at 19A all day, every day, for years and have had no problems.

  5. #5
    Join Date
    Sep 2004
    Location
    San Jose
    Posts
    66
    Quote Originally Posted by Jacob Wall View Post
    I've seen people run a 20A circuit at 19A all day, every day, for years and have had no problems.
    Some people get away with it. Others do not. For every 20A circuit I see at 19A, I see another one running at 18A that trips on occasion.
    Steve Rubin - ser@layer42.net
    Layer42 Networks - http://www.Layer42.net/

  6. #6
    Join Date
    Dec 2007
    Location
    Isle of Man
    Posts
    3,068
    Quote Originally Posted by ST-3 View Post
    Some people get away with it. Others do not. For every 20A circuit I see at 19A, I see another one running at 18A that trips on occasion.
    Precisely, it's risky and can be an expensive risk to take.

  7. #7
    In a data center it's not going to matter whether you can or not.

    You won't be permitted to run steady state at more than 80 percent of the ciruit rating. If you don't reduce the load when asked, they'll just shut you down until you do.
    edgedirector.com
    managed dns global failover and load balance (gslb)
    exactstate.com
    uptime report for webhostingtalk.com

  8. #8
    Quote Originally Posted by shunter1 View Post
    So, I understand, the rule of 80% to be to the effect that "during startup, equipment uses more power ... or during runtime if it heats up, the fans go faster using more power" so it is safe to be at 24A in case you get spikes to 27-29A.
    Start-up power is nothing compared to what you will be drawing with your CPUs fully loaded--at least with quads and dual quads.

  9. #9
    Join Date
    Mar 2006
    Location
    Reston, VA
    Posts
    3,131
    Coresite slaps you with a $500/fee if you go over 80% on your circuits.. each.. time... its called their "branch circuit monitoring"
    Yellow Fiber Networks
    http://www.yellowfiber.net : Managed Solutions - Colocation - Network Services IPv4/IPv6
    Ashburn/Denver/NYC/Dallas/Chicago Markets Served zak@yellowfiber.net

  10. #10
    Join Date
    Aug 2003
    Location
    /dev/null
    Posts
    2,132
    Anyway, it's still illegal...

  11. #11
    Join Date
    Mar 2009
    Posts
    2,222
    Quote Originally Posted by shunter1 View Post
    So the rule of thumb is if you have a 30A circuit to not exceed 80% or 24A.
    No, you can't go by rules of thumb for data centres; you have to ask the electrical engineer what the limit is for your circuits.

    Personally, I would expect a 30-amp supply to have a 30-amp breaker, and be capable of delivering up to 30 amps continuously. The US wiring regulations allow this, provided the underfloor cables are adequate. But what is adequate depends on the temperature rating of the underfloor cables, and how many cables there are per cableway. That's why you have to ask the electrical engineer what the limit is.

    However, if the power strip is shared with other customers, the data centre management will likely impose an 80% limit for management purposes - to reduce the risk of one customer overloading the strip and taking out other customer's equipment (imagine a rack running fine, till some customer upgrdes all their servers with extra memory, disks, CPUs ...). And even if you are the only person using the cabinet, they may still impose a limit to keep the air conditioning within its capacity.

    By the way, electrical engineers do not necessarily know how server power supplies work; you may have to explain that for a dual-powered server, the load is normally split equally between the two power supplies. If one can no longer deliver power, its load will instantly be taken by the other; the overall load will likely *fall* slightly, because the server's power supply will be operating at a higher load hence higher efficiency.
    Last edited by tim2718281; 10-18-2009 at 09:57 PM.

  12. #12
    Join Date
    Aug 2005
    Location
    PA
    Posts
    324
    The problem is that you are assuming that the electrical equipment is in-spec all the time.

    The 80% is partially to avoid cases where the sum of all the components in the power feed trip. That is, you might buy two different circuit breakers - the manufacturing tolerance is so wide that one might go at 90% continuous load all the time, the other might trip at 81% continuous load.

    Which part is "bad"?

    Actually they are both OK from the standpoint of the NEC.

    Remember too that there is some resistance at each point and the purpose is to avoid there being too much warmth which could cause a fire.
    reliable colocation ... Dedicated Servers | Dedicated Server VMs | FAST links to Vitelity.com and Conexiant.net
    patrick@zill.net Cell +1.717.201.3366

  13. #13
    Join Date
    Mar 2009
    Posts
    2,222
    Quote Originally Posted by MrZillNet View Post
    Remember too that there is some resistance at each point and the purpose is to avoid there being too much warmth which could cause a fire.
    Wiring regulations or standards will specify a maximum permitted voltage drop, thus limiting the heat generated.

    Typically the max voltage permitted drop will be 2%; so, in the case of 120V 30 amps, the load is 4 ohms, and a 2% voltage drop means the cabling resistance is 0.08 ohms, and so the power dissipation within the cable will be 72 watts, distributed alonmg the length of the cable ... maybe 2 watts per foot.

    But put a number of cables together in a cable tray and you can see how the heat can build up; which is why the wiring regulations stipulate increasing thickness of cables (hence less voltage drop and resistance) where there are higher numbers of cables in a tray.

  14. #14
    Join Date
    Mar 2009
    Location
    $HOME
    Posts
    85
    Quote Originally Posted by tim2718281 View Post
    I would expect a 30-amp supply to have a 30-amp breaker, and be capable of delivering up to 30 amps continuously. The US wiring regulations allow this, provided the underfloor cables are adequate.
    A helpful overview of when 100%-rated breakers is permissible is

    http://static.schneider-electric.us/...0600DB0101.pdf

    I have only seen 100%-rated breakers in distribution circuits of 200A or more, usually when the branch circuit is a longer length. At the branch circuit level, it's cheaper to move to a larger amperage, higher voltage, or more phases.

    But I have a feeling this discussion isn't about what is permissible per code, but rather why you can't use that extra 25% capacity. Thankfully, the world is moving to usage-based power billing, so hopefully we will lose the unhelpful incentive to pack as much as possible onto a branch circuit.

  15. #15
    Join Date
    Mar 2009
    Location
    $HOME
    Posts
    85
    In Tier-2 designs, it may be permissible to have primary and redundant circuits loaded to 50%, depending on who you ask (heck, if it's your own datacenter, load them both to 80% if you like, so they pop during your first failover... it's a free country!). But to meet Tier-3 criteria, no power system component may exceed 90%, even when operating in Maintenance Mode (e.g. primary circuit taken off-line for maintenance). So that would limit load to 45% on each of primary and redundant, in Tier-3 datacenters.

  16. #16
    Quote Originally Posted by Spudstr View Post
    Coresite slaps you with a $500/fee if you go over 80% on your circuits.. each.. time... its called their "branch circuit monitoring"
    Damn Zak - that's crazy.
    --
    I'm retired.
    Check out http://yellowfiber.net for all your needs!

  17. #17
    Join Date
    Feb 2004
    Location
    Atlanta, GA
    Posts
    5,662
    Quote Originally Posted by PhPhear View Post
    Damn Zak - that's crazy.
    Thats not such a bad policy, if a customer was to have sustained "violations" as opposed to a 10 minute spike into 80%+ or some short period that is caused by increased activity or something of that nature.

    Basically it's a good heavy handed method to force compliance. It was always amusing to me to walk around in the facility we colo'd in before we got our own and see what other colocation customers were doing, there was always one in particular that was riding 90% all day long and you would always seem them tripping circuits.

    I guess to some people that extra 10% usage really helps their bottom line? (until the outage comes) lol...

Similar Threads

  1. Circuit City Short Circuits
    By RandyT in forum Web Hosting Lounge
    Replies: 13
    Last Post: 11-06-2008, 01:52 AM
  2. Cogent redundent circuits?
    By Spudstr in forum Colocation, Data Centers, IP Space and Networks
    Replies: 12
    Last Post: 12-18-2006, 01:59 PM
  3. Best price on MCI circuits
    By oana_maria in forum Colocation, Data Centers, IP Space and Networks
    Replies: 5
    Last Post: 09-06-2006, 12:23 PM
  4. How to monitor PR1 circuits ?
    By chefwong in forum Hosting Security and Technology
    Replies: 1
    Last Post: 02-05-2006, 12:34 PM
  5. Anyone in here know how to do circuits
    By Kit in forum Web Hosting Lounge
    Replies: 11
    Last Post: 09-14-2003, 09:35 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •