    is 28'c ok for colo ?


    im looking for a new DC,

    it's temperature is about 28'c,

    will it be too high for colo?


  2. #2
    Join Date
    Apr 2002
    North Kansas City, MO
    28 is a little high. 22 is about right for a Datacenter
    Aaron Wendel
    Wholesale Internet, Inc. -
    Kansas City Internet eXchange -

  3. #3

    Different opinions for data center temperature

    It really depends on air-flow, which seems to be the more important factor here.

    There's some really good articles that you can read online about data center temperature - just type in 'temperature for datacenter' in a serch engine, and there are many articles discussing datacenters running equipment fine at temperatures between 80-85F (>28C).

  4. #4
    Join Date
    Aug 2006
    Also have a go at reading this when you have the time:
    Ekin Ersoy
    Stagnom Servers | Europe Dedicated Servers with Redefined Support
    Follow us on Twitter: @StagnomUK | Like us on Facebook:

  5. #5
    Join Date
    May 2005
    New York
    also whether you are talking about ambient temperature in an open-flow air conditioned room (where the same air circulation is present at intake + exhausts) - or a hot-aisle/cold-aisle setup, where the ambient is somewhere in between the cold aisle & hot aisle or about 75% of the way towards the hot (if cold is shielded).

    In setup one - a 28 ambient means the air going in to your cabinet is about 25 or 26, and the exhaust is possibly 35. in a hot/cold aisle setup, the intakes would likely be 20, with the exhausts about 32. In bot h scenarios you would probably want to keep your power density pretty low - talking < 2.5kVA per cabinet to be safe (dependant on your server tolerances of course) - really depends on the design of the colo
    Perigee Global Corporation
    Design, Development and Hosting Solutions
    Dedicated Servers, CDN, Hosted E-Mail, Web Hosting, VPS & Cloud Servers

  6. #6
    Join Date
    Apr 2007
    You don't really want higher than 24'c
    Sounds high to me, although equipment will probably run fine.
    - Buying up websites, side-projects and companies - PM Me! -

  7. #7
    Join Date
    Mar 2001
    Depends on the layout of the data centre - If it's 28 degrees in a hot aisle with separation between it and the cold aisle then it should be fine (Do you know the temperature across the front of the rack or the server in-let temperatures?)

    Also it might be worth bearing in mind that under the Ashrae guidelines for data centres that 28 degree is just outside of the recommended limits by 1 degree but still well within the allowable ranges (There are a few facilities, mainly in the States as far as I know, that are trailing no air-con and using ambient air to pull through servers).
    David Barker
    4D Data Centres - Independent UK based data centre operator

Similar Threads

  1. Fremont Colo, Las Vegas Colo, Los Angeles Colo, $0 Setup Fees
    By Ivan23 in forum Colo Hosting Offers
    Replies: 0
    Last Post: 05-16-2008, 10:34 PM
  2. Replies: 2
    Last Post: 05-28-2007, 02:22 PM
  3. Replies: 12
    Last Post: 05-15-2007, 01:22 PM
  4. Replies: 9
    Last Post: 11-15-2006, 08:39 PM
  5. Replies: 0
    Last Post: 04-09-2004, 03:15 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts