Colocation and Data Centers Find data centers, server hardware, bandwidth providers, and techniques for colocation purposes. Get advice on colocation web hosting, review providers and offer suggestions on choosing colocation hosting services and the right datacenter. If your service is unavailable, please click here.
Forum Jump

Little help determining power draw please.

Reply Post New Thread In Colocation and Data Centers Subscription
 
Send news tip View All Posts Thread Tools Search this Thread Display Modes
  #1  
Old 01-01-1970, 12:00 AM
jbs192 jbs192 is offline
Newbie
 
Join Date: Feb 2008
Posts: 8
If you had to rack 100 x Dell PE 2950 2x Quad Core 2.33GHz boxes. How many of what type of power circuits would you ask the colocation provider to quote?

Reply With Quote


Sponsored Links
  #2  
Old 01-01-1970, 12:00 AM
accidental uptime accidental uptime is offline
Newbie
 
Join Date: Sep 2008
Location: Boston
Posts: 19
The specs on Dells site don't indicate the max Amp draw but @ 220v it looks like they'll draw around 3 amps each. Your looking at 300 amps if they can provide you with 220v circuits.
You may want to get the max amp draw from Dell if you can for a more accurate picture.

Reply With Quote
  #3  
Old 01-01-1970, 12:00 AM
avizzle avizzle is offline
Junior Guru
 
Join Date: Mar 2005
Posts: 222
Every 1950, or 2950 has used between 1.5 to 2.5A depending on load at 110v.
If you assume the high end of 2.5A, multiply that by 100 then you have 250A. That's going to require you to get at least 312.5A to comply with the 80% draw rule. No one I know sells 12.5A circuits, so I would assume you would need a 20 for that, for a total of 320A.
I didn't check, but are those low voltage Xeons? If they are, they will use about 1 to 1.5A.

Reply With Quote
Sponsored Links
  #4  
Old 01-01-1970, 12:00 AM
avizzle avizzle is offline
Junior Guru
 
Join Date: Mar 2005
Posts: 222
To add, we have something here at the office called a Kill-A-Watt, its a power draw meter that plugs directly into the wall which you can use to accurately determine power usage.
Check it out: http://www.newegg.com/Product/Product.aspx?Item=N82E16882715001

Reply With Quote
  #5  
Old 01-01-1970, 12:00 AM
johnbrown362003 johnbrown362003 is offline
WHT Addict
 
Join Date: Jul 2005
Posts: 172
Have you used the dell power calculator at www.dell.com/calc
Also you will need to adjust your power calculation depending on the memory .

Reply With Quote
  #6  
Old 01-01-1970, 12:00 AM
jbs192 jbs192 is offline
Newbie
 
Join Date: Feb 2008
Posts: 8
Thanks for your help guys... Got what I needed.

Reply With Quote
  #7  
Old 01-01-1970, 12:00 AM
Webdude Webdude is offline
Web Hosting Master
 
Join Date: Dec 2000
Location: The Woodlands, Tx
Posts: 5,955
To add, we have something here at the office called a Kill-A-Watt, its a power draw meter that plugs directly into the wall which you can use to accurately determine power usage.
Check it out: http://www.newegg.com/Product/Product.aspx?Item=N82E16882715001
I wonder if they have those for the bigger twist-lock applications.

Reply With Quote
  #8  
Old 01-01-1970, 12:00 AM
Justin M
Guest
 
Posts: n/a
I wonder if they have those for the bigger twist-lock applications.
http://us.fluke.com/usen/products/Fluke+320.htm
Like that?

Reply With Quote
  #9  
Old 01-01-1970, 12:00 AM
Webdude Webdude is offline
Web Hosting Master
 
Join Date: Dec 2000
Location: The Woodlands, Tx
Posts: 5,955
Well, was thinking a little more of a permanant fixture... but I had forgotten about those which would work for quick checks.

Reply With Quote
  #10  
Old 01-01-1970, 12:00 AM
AoW AoW is offline
Junior Guru Wannabe
 
Join Date: Feb 2004
Location: Barcelona, Spain
Posts: 30
With 220V calculate about 1.25A - 1.5A per server. Also, deppends on HDs and RAM.
A safer value would be 1.75A.
Also deppends if you are going to keep these boxes in a high load.

Reply With Quote
  #11  
Old 10-17-2008, 04:39 PM
jbs192 jbs192 is offline
Newbie
 
Join Date: Feb 2008
Posts: 8
If you had to rack 100 x Dell PE 2950 2x Quad Core 2.33GHz boxes. How many of what type of power circuits would you ask the colocation provider to quote?

Reply With Quote
  #12  
Old 10-17-2008, 04:51 PM
accidental uptime accidental uptime is offline
Newbie
 
Join Date: Sep 2008
Location: Boston
Posts: 19
The specs on Dells site don't indicate the max Amp draw but @ 220v it looks like they'll draw around 3 amps each. Your looking at 300 amps if they can provide you with 220v circuits.
You may want to get the max amp draw from Dell if you can for a more accurate picture.

Reply With Quote
  #13  
Old 10-17-2008, 05:16 PM
avizzle avizzle is offline
Junior Guru
 
Join Date: Mar 2005
Posts: 222
Every 1950, or 2950 has used between 1.5 to 2.5A depending on load at 110v.
If you assume the high end of 2.5A, multiply that by 100 then you have 250A. That's going to require you to get at least 312.5A to comply with the 80% draw rule. No one I know sells 12.5A circuits, so I would assume you would need a 20 for that, for a total of 320A.
I didn't check, but are those low voltage Xeons? If they are, they will use about 1 to 1.5A.

Reply With Quote
  #14  
Old 10-17-2008, 05:17 PM
avizzle avizzle is offline
Junior Guru
 
Join Date: Mar 2005
Posts: 222
To add, we have something here at the office called a Kill-A-Watt, its a power draw meter that plugs directly into the wall which you can use to accurately determine power usage.
Check it out: http://www.newegg.com/Product/Product.aspx?Item=N82E16882715001

Reply With Quote
  #15  
Old 10-18-2008, 02:55 PM
johnbrown362003 johnbrown362003 is offline
WHT Addict
 
Join Date: Jul 2005
Posts: 172
Have you used the dell power calculator at www.dell.com/calc
Also you will need to adjust your power calculation depending on the memory .

Reply With Quote
Reply

Related posts from TheWhir.com
Title Type Date Posted
Data Center Solutions Firm Active Power Names VP of Engineering Web Hosting News 2011-11-23 20:51:37
Active Power Names Interim President and CEO Following Jim Clishem's Resignation Web Hosting News 2011-10-18 17:01:39
Level 3 Upgrades London, Amsterdam Data Centers to Renewable Energy Web Hosting News 2011-08-30 20:02:27
Power Assure CTO: Some Efficiency Ratings Miss Incremental Improvements Web Hosting News 2011-08-18 18:57:44
Colocation Firm Internap Expands Atlanta Data Center Web Hosting News 2011-07-27 17:02:55


Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes
Postbit Selector

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is Off
HTML code is Off

Forum Jump
Login:
Log in with your username and password
Username:
Password:



Forgot Password?
Advertisement:
Web Hosting News:



 

X

Welcome to WebHostingTalk.com

Create your username to jump into the discussion!

WebHostingTalk.com is the largest, most influentual web hosting community on the Internet. Join us by filling in the form below.


(4 digit year)

Already a member?