Colocation and Data Centers Find data centers, server hardware, bandwidth providers, and techniques for colocation purposes. Get advice on colocation web hosting, review providers and offer suggestions on choosing colocation hosting services and the right datacenter. If your service is unavailable, please click here.
Forum Jump

Liebert UPS Efficiency

Reply Post New Thread In Colocation and Data Centers Subscription
 
Send news tip View All Posts Thread Tools Search this Thread Display Modes
  #1  
Old 10-15-2007, 08:41 PM
KarlZimmer KarlZimmer is offline
THE Web Hosting Master
 
Join Date: Jan 2003
Location: Chicago, IL
Posts: 6,545

Liebert UPS Efficiency


Hello everyone,
I was wondering if anyone with some experience running facilities, etc. is familiar with how much power a 750kVa Liebert UPS will use when it is under minimal load. I am aware that power is needed for keeping the batteries charged, keeping the power levels consistent, etc. but what is that base amount? Then, at around full load, what efficiency levels can I expect?

If it helps, I believe the model # for the specific unit is FRUDA63750A36A3

__________________
Karl Zimmerman - Steadfast Networks: Dedicated Servers and Premium Colocation
karl @ steadfast.net - AIM: KarlAZimmerman - Sales/Support: 312-602-2689
2 Data Centers and 20,000+ sqft. in Chicago (350 E Cermak) + Manhattan Data Center
Cloud Hosting, Managed Dedicated Servers, Chicago Colocation, and New York Colocation

Reply With Quote


Sponsored Links
  #2  
Old 10-15-2007, 08:47 PM
jayglate jayglate is offline
Doh!!
 
Join Date: Jan 2001
Location: NJ
Posts: 2,294
You get much better efficiency by going with 2 or 3 smaller units than 1 big unit.

__________________
Jason Silverglate jason [.at.] fortressitx.com
DedicatedNOW Managed Dedicated Servers / | 1-973-572-1070 support ext for 24/7 LIVE SUPPORT
Celebrating 12 years in business! Privately Owned Datacenter metro NYC Dark Fiber Ring and more!

Reply With Quote
  #3  
Old 10-15-2007, 08:54 PM
KarlZimmer KarlZimmer is offline
THE Web Hosting Master
 
Join Date: Jan 2003
Location: Chicago, IL
Posts: 6,545
Quote:
Originally Posted by jayglate View Post
You get much better efficiency by going with 2 or 3 smaller units than 1 big unit.
I know that much, but I'm looking at an existing facility and doing some base cost analysis, etc. as I want the space, but don't need much of it immediately. Wondering how much the 2 750kVA units are going to cost me on my electric bill.

__________________
Karl Zimmerman - Steadfast Networks: Dedicated Servers and Premium Colocation
karl @ steadfast.net - AIM: KarlAZimmerman - Sales/Support: 312-602-2689
2 Data Centers and 20,000+ sqft. in Chicago (350 E Cermak) + Manhattan Data Center
Cloud Hosting, Managed Dedicated Servers, Chicago Colocation, and New York Colocation

Reply With Quote
Sponsored Links
  #4  
Old 10-15-2007, 10:32 PM
sailor sailor is offline
cloud beats dedicated ;)
 
Join Date: Dec 2001
Location: Atlanta
Posts: 4,419
Quote:
Originally Posted by KarlZimmer View Post
I know that much, but I'm looking at an existing facility and doing some base cost analysis, etc. as I want the space, but don't need much of it immediately. Wondering how much the 2 750kVA units are going to cost me on my electric bill.
35 to 50 kva per unit will be used with it just idling.

__________________
Experience the real cloud at GNAX
WWW.GNAX.NET
VMWare based cloud
Isn't it time to get off of dedicateds?

Reply With Quote
  #5  
Old 10-16-2007, 12:01 AM
Linn_Boyd Linn_Boyd is offline
Web Hosting Evangelist
 
Join Date: Nov 2004
Location: Atlanta, GA
Posts: 454
Sailor hit it about dead on, you are going to need to also replace the batteries if it has been sitting for any amount of time.

-Linn

__________________
Linn Boyd

Reply With Quote
  #6  
Old 10-16-2007, 12:02 AM
Jay Suds Jay Suds is offline
Web Hosting Master
 
Join Date: Jun 2001
Location: Denver, CO
Posts: 3,210
If the units are currently running [with no load], take an ammeter over there and find out how many amps the units are pulling. Or drag your electrician over there with you, and let him do it.

__________________
Jay Sudowski // Handy Networks LLC // Co-Founder & CTO
AS30475 - Level(3), HE, Telia, XO and Cogent. Noction optimized network.
Offering Self Managed, Truly Dedicated Server and Colocation from our Private Denver Data Center.
Current specials here. Check them out.

Reply With Quote
  #7  
Old 10-16-2007, 01:00 AM
scapeish scapeish is offline
Junior Guru
 
Join Date: Jun 2007
Posts: 188
A quick question related to this thread but not covered within it; slightly off topic.

Is it industry standard to run the UPS constantly wth minimal load in order to prsever batteries, or would the extremely light load nonetheless drain the batteries chemical life (not the amount of power contained within)? Sorry for the off topic, but I'm hesitat to make changes before I have multiple industry experts' second & third opinions. Thanks for the reply.

Reply With Quote
  #8  
Old 10-16-2007, 01:17 AM
sailor sailor is offline
cloud beats dedicated ;)
 
Join Date: Dec 2001
Location: Atlanta
Posts: 4,419
Quote:
Originally Posted by scapeish View Post
A quick question related to this thread but not covered within it; slightly off topic.

Is it industry standard to run the UPS constantly wth minimal load in order to prsever batteries, or would the extremely light load nonetheless drain the batteries chemical life (not the amount of power contained within)? Sorry for the off topic, but I'm hesitat to make changes before I have multiple industry experts' second & third opinions. Thanks for the reply.
the load on the ups has nothing to do with the battreries per your application. when the ups is on and the battery breakers are closed it will keep them charged and give them a longer life.

the only thing that drains batteries and shortens life is:

unbalanced strings due to mix matching battery types and ages and or lots

leaving them in a state of discharge

not keeping them charged for long periods of time

not hitting them every now and then with a load discharge that will knock the dust of the plates (not really dust - its a buildup though)

__________________
Experience the real cloud at GNAX
WWW.GNAX.NET
VMWare based cloud
Isn't it time to get off of dedicateds?

Reply With Quote
  #9  
Old 10-16-2007, 01:21 AM
sailor sailor is offline
cloud beats dedicated ;)
 
Join Date: Dec 2001
Location: Atlanta
Posts: 4,419
Quote:
Originally Posted by TheDingy View Post
Sailor hit it about dead on, you are going to need to also replace the batteries if it has been sitting for any amount of time.

-Linn

that is correct. depending on the units age - you also might have to replace the ac and dc caps.

the dc caps are a little more tempramental - they will absolutely need to be replaced if the unit is 5 or more years old and they have not been replaced before.

you can usually call liebert and they can give oyu the service history or the guys taking care of it will usually have their sticker on it somewhere.

both can be expensive.

also visually inspect your transformer rappings including the main transformers and any neutral harmonic isolation chokes if you equipment comes with them. they should be honey colored - if they are white they are fried and will need to be replaced.

listen to the fans and make sure they are all working.

finally check and make sure the system is giving no warnings and will run through the complete output on the oneline interface or you could also have a fried logic board.

as another poster says - check the draw on the 3 legs and make sure it is balanced - if not it could indicate many problems,

p.s. if you dont have a full maintenance wraparound bypass on the unit you would be well advised to install one while the unit is out of service. if you ever need to do anything to it in the future when you are loaded - you will hate life if you have to drop your load to service it- ie replace a transformer or such, i have replaced a transformer on a liebert unit - luckily it had a full wrap on it so the load did not have to be dropped.

good luck with them.

__________________
Experience the real cloud at GNAX
WWW.GNAX.NET
VMWare based cloud
Isn't it time to get off of dedicateds?


Last edited by sailor; 10-16-2007 at 01:24 AM.
Reply With Quote
  #10  
Old 10-16-2007, 01:55 AM
Jay Suds Jay Suds is offline
Web Hosting Master
 
Join Date: Jun 2001
Location: Denver, CO
Posts: 3,210
Full bypass wrap around is a necessity. Having to drop your load to do maintenance (routine or non-routine) is obviously quite lame.

Battery life will also shorten if you don't have proper cooling in your UPS room. You don't want to skimp on cooling your batteries. They are a real, on-going expense and you don't want to have to incur that expense every 3 years instead of every 5 years because you keep your UPS room at 95 degrees.

On the topic of fans ... we had one go in our Mitsubishi 375kva UPS and it was nearly $3000 to get a new one. Nearly choked on my lunch when I opened that invoice up. Obviously, not a ton of money, but I was just astounded by how much a stupid fan cost.

__________________
Jay Sudowski // Handy Networks LLC // Co-Founder & CTO
AS30475 - Level(3), HE, Telia, XO and Cogent. Noction optimized network.
Offering Self Managed, Truly Dedicated Server and Colocation from our Private Denver Data Center.
Current specials here. Check them out.

Reply With Quote
  #11  
Old 10-18-2007, 06:19 PM
WII-Aaron WII-Aaron is offline
Community Guide
 
Join Date: Apr 2002
Location: Kansas City, MO
Posts: 2,241
Quote:
Originally Posted by jayglate View Post
You get much better efficiency by going with 2 or 3 smaller units than 1 big unit.
I disagree with you. At full load with an efficiency of 95% it makes no difference weather you have 1 750kVA or 5 150kVA units. Efficiency is the same.

on the low end, while smaller UPS units give you more diversity and resilliance you'll be screwed on efficiency unless you can pull more then 40KW per unit.

A 750kVA Powerware 9315 pulls 44KW minimum and a 160kVA Powerware 9315 pulls 37KW minimum. 37 X 5 is alot more then 44.

I know the thread is about Lieberts but I use the Powerware as examples because the above units are ones I actually own.

Aaron

__________________
Aaron Wendel
Wholesale Internet, Inc. - http://www.wholesaleinternet.net
Kansas City Internet eXchange - http://www.kcix.net

Reply With Quote
  #12  
Old 10-24-2007, 03:58 PM
RackMy.com RackMy.com is offline
Web Hosting Master
 
Join Date: Apr 2001
Location: St. Louis, MO
Posts: 2,508
Quote:
not hitting them every now and then with a load discharge that will knock the dust of the plates
When you "hit" them with a load discharge you are shortening the length of the batteries. Everytime you go to batts you are decrease it's total capacity.

Quote:
You get much better efficiency by going with 2 or 3 smaller units than 1 big unit.
One larger unit at full load will be more efficient that several smaller units. That being said, I would never one one UPS in a critical DC environment. It's a single point of failure.

__________________
Mike @ Xiolink.com
http://www.xiolink.com 1-877-4-XIOLINK
Advanced Managed Microsoft Hosting
"Your data... always within reach"

Reply With Quote
Reply

Related posts from TheWhir.com
Title Type Date Posted
The Green Grid to Host Forum 2013 in Santa Clara Web Hosting News 2013-01-08 14:13:07
The Green Grid Launches Module to Help Users Understand, Apply DCEE Tools Web Hosting News 2012-08-21 16:48:42
Green Grid, Open Data Center Alliance to Drive Efficient Cloud Standards Web Hosting News 2011-11-09 15:03:49
Colocation Firm Waveform Upgrades Michigan Data Center Web Hosting News 2011-10-07 19:52:29
Power Assure CTO: Some Efficiency Ratings Miss Incremental Improvements Web Hosting News 2011-08-18 18:57:44


Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes
Postbit Selector

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is Off
HTML code is Off

Forum Jump
Login:
Log in with your username and password
Username:
Password:



Forgot Password?
Advertisement:
Web Hosting News:



 

X

Welcome to WebHostingTalk.com

Create your username to jump into the discussion!

WebHostingTalk.com is the largest, most influentual web hosting community on the Internet. Join us by filling in the form below.


(4 digit year)

Already a member?