Colo for 400mbit commit/ full 42u rack/2x20amp
Hi,
What will it cost for the following in Central NJ.
- 400mbit commit
- Full 42u Locked rack
- 2x20amp power
Im looking to put 40x1u severs with 10mbit dedicated ports w/unlimited bandwidth per server.
Also, will 2x20amp be enough power? Each server is 325watt i think. PowerEdge 1750.
Whats the going rate for quality commits from 100mbit to 500mibt? Whats the rate for ok commits?
Thanks,
Calvin
-
09-30-2006, 01:47 AM #2Managed Service Provider
- Join Date
- Feb 2004
- Location
- Atlanta, GA
- Posts
- 5,662
325W / 110V = ~2.95A / server MAX draw
To get that kind of density in a single cabinet 208V/220V/240V or what ever they are supplying would be your best option.
2 x 20A will certainly not be enough.
-
09-30-2006, 02:01 AM #3Web Hosting Master
- Join Date
- Oct 2005
- Location
- United States
- Posts
- 1,405
40amps should work for 20-30 servers.
The cost of bw depends on the kind of bw. What DC will you co-locate your servers?Tommy Tran - tommy @ vinax.net ::: VINAX, LLC ::: http://vinax.net ::: Since 2004
Premium Dedicated Servers and Colocation in downtown Chicago (350 E. Cermak Rd)
Premium Bandwidth, 100% Network & Power Uptime SLA, 24/7 Prompt Tech Support
-
09-30-2006, 10:22 AM #4Randy
- Join Date
- Aug 2006
- Location
- Ashburn VA, San Diego CA
- Posts
- 4,615
You can get Cogent bandwidth at >100Mbps commits for $12.00 to $15.00 per Mbps depending on provider, assuming you do not go directly to cogent in which case you could get $10.00 per Mbps on 200+Mbps commits. I wouldn't recommend colocating directly with Cogent for several reasons.
Ideally you want a blend of cogent and other providers which many colo's can provide. Expect to pay $13.00 per Mbps or more for 400Mbps commits, from a quality provider with good support and uptime. You'll probably pay more per Mbps for lower commits, possibly $15.00 - $20.00.
Are you dead set on NJ? What about VA?Fast Serv Networks, LLC | AS29889 | DDOS Protected | Managed Cloud, Streaming, Dedicated Servers, Colo by-the-U
Since 2003 - Ashburn VA + San Diego CA Datacenters
-
09-30-2006, 10:23 AM #5Newbie
- Join Date
- Sep 2006
- Location
- New Jersey
- Posts
- 17
Hey thanks,
What does that much power usually cost per cabinet?
As for what DC i will be colocated, I prefer NJ. I was in NY before, it was a pain to get to. Im in NJ now, but its still a pain to get to since its further then NY now.
I know there isnt much colos in central NJ besides Jersey City, Secaucus...etc
Are there any colos down by Edison. NJ, Freehold, area?
Thanx,
Calvin
-
09-30-2006, 10:31 AM #6Newbie
- Join Date
- Sep 2006
- Location
- New Jersey
- Posts
- 17
Oups, hehe, FastServ, you posted when I just replied so I didnt read your post till now.
Hmm, 15mbit commit for quality connection is not too bad. Ive been with Cogent in NY. Nice facility. I am now in NJ. It actually further to get thru now. Hehehe. I wanted to be able to go there anytime during the day. I didnt do that in NY because of parking in the day time. Too expensive. And no street parking.
Im really looking for something close. Any idea exaclty what a
42u locked cabinet
208V/220V/240V power (WireSix suggested above)
400mbit
will cost at a colo in NJ?
Like i stated above, i am looking to colocate max of 40 1u servers each with 325watt power. My goal is to supply 10mbit ports to each server.
Thanks again all,
Calvin
-
09-30-2006, 10:52 AM #7Junior Guru
- Join Date
- Jul 2003
- Location
- Connecticut
- Posts
- 230
have you talked to NAC.net? they do Colo and are in NJ.. very good network.
-
09-30-2006, 11:03 AM #8Web Hosting Master
- Join Date
- Nov 2002
- Posts
- 2,780
Interserver.net is in NJ. You are probably looking at 7K or so
http://Ethr.net jay@ethr.net
West Coast AT&T / Level3 / Savvis Bandwidth, Colocation, Dedicated Server, Managed IP Service, Hardware Load Balancing Service, Transport Service, 365 Main St, SFO / 200 Paul Ave, SFO / PAIX, PAO / Market Post Tower, 55 S. Market, SJC / 11 Great Oaks, Equinix, SJC
-
09-30-2006, 01:01 PM #9Master of the Truth
- Join Date
- Mar 2006
- Location
- Reston, VA
- Posts
- 3,131
Theres two equinix buildings in NJ, Newwark and Saccacus.. as far as providers.. i'm sure cogent is in one or both of those locations.
Yellow Fiber Networks
http://www.yellowfiber.net : Managed Solutions - Colocation - Network Services IPv4/IPv6
Ashburn/Denver/NYC/Dallas/Chicago Markets Served zak@yellowfiber.net
-
09-30-2006, 03:57 PM #10Web Hosting Master
- Join Date
- Nov 2002
- Posts
- 2,780
165 Halsey, in Equinix Newark
275 Hartz, is in Secaucus
The Secaucus one is state of the art, probably still have room. Halsey is full.http://Ethr.net jay@ethr.net
West Coast AT&T / Level3 / Savvis Bandwidth, Colocation, Dedicated Server, Managed IP Service, Hardware Load Balancing Service, Transport Service, 365 Main St, SFO / 200 Paul Ave, SFO / PAIX, PAO / Market Post Tower, 55 S. Market, SJC / 11 Great Oaks, Equinix, SJC
-
09-30-2006, 08:17 PM #11Web Hosting Master
- Join Date
- Sep 2005
- Posts
- 551
I believe there is at least one datacenter in Clifton NJ
-
09-30-2006, 08:54 PM #12Disabled
- Join Date
- Jan 2006
- Posts
- 388
You do realize to use those voltages in power feeds, your power supplies in the servers, and your power stips will need to support it, unless you plan on running your very own PDU and converting the voltage back down to appropriate amounts for power strip/PSU
It'll be cheaper to just get 3 x 20AMP circuits.
You are also going to need 3 x 0U vertical power strips.
-
09-30-2006, 09:01 PM #13Retired Moderator
- Join Date
- Apr 2005
- Posts
- 3,499
Originally Posted by MSV_AR
Alex
-
09-30-2006, 10:21 PM #14Doh!!
- Join Date
- Jan 2001
- Location
- NJ
- Posts
- 2,343
Originally Posted by MSV_ARJay
-
09-30-2006, 10:47 PM #15Web Hosting Master
- Join Date
- Feb 2004
- Posts
- 963
Originally Posted by xoopa
Another concern I would have is that those power edge 1750s run VERY hot. A customer of mine had 6 racks, each with 28 per rack, in big racks (30" wide, 42" deep) and it felt ovenlike walking behind them. They don't have enough airflow with those 3 drives in the front, and we were losing an unusual amount of disks. Dell's claim was the heat was causing the hotplug backplanes to push the disks out just enough that the PERC card would think they had failed.
-
10-01-2006, 12:24 AM #16Newbie
- Join Date
- Sep 2006
- Location
- New Jersey
- Posts
- 17
Hi,
I see a few racks with PE 1750s in them. Pretty much filled the whole 42u rack.
I wonder how they were able to get that much power in there. I didnt know they ran that hot.
Whats the ideal amount of 1u servers to per 42u rack? I have 12 pe 2650 and 2 pe 2550 on a 42u rack currently, but they take up twice the space as the 1750s.
I havent had any trouble with them though. WIll the pe 1750s be troublesome?
Better to stick with 2650s? They are 500watt power. Im on a 20amp line. They seem fine. I guess I shouldnt be running more then 30 per rack? Man, it gonna be tough to offer low cost 1u servers with dedicated 10mbit commits.
Thanks again,
Calvin
-
10-01-2006, 12:47 AM #17Web Hosting Master
- Join Date
- Aug 2002
- Location
- London, UK
- Posts
- 9,039
You would likely be best off looking for 2 racks for your power requirement and running them slightly empty rather than stuffing 40 into a single rack.
Dell's arent too good for power so you will struggle. Buying better hardware or LV cpu's could save on power month on month but obviously higher costs to purchase up front.
-
10-01-2006, 01:36 AM #18Retired Moderator
- Join Date
- Apr 2005
- Posts
- 3,499
Now that I think about it a little bit more, it may be more ideal to buy 2 cabinets. That way you can get 2x20amp circuits (1 per cab) and have your servers spaced nicely so that cooling is not such a big issue. Also, you have more room for expansion should the time come.
Alex
-
10-01-2006, 03:13 AM #19Backup Guru
- Join Date
- Feb 2002
- Location
- New York, NY
- Posts
- 4,618
Originally Posted by xoopa
10 would be a more realistic number, or 15 if you want to have a warm cabinet.Scott Burns, President
BQ Internet Corporation
Remote Rsync and FTP backup solutions
*** http://www.bqbackup.com/ ***
-
10-01-2006, 05:42 AM #20Web Hosting Master
- Join Date
- Nov 2001
- Location
- London
- Posts
- 4,931
Originally Posted by FR-AlexMatthew Russell | Namecheap
Twitter: @mattdrussell
www.easywp.com - True Managed WordPress, made easy
-
10-01-2006, 08:32 AM #21Disabled
- Join Date
- Jan 2006
- Posts
- 388
Originally Posted by bqinternet
325W is the max for that PSU, they won't be pushing that consistantly.
---
If you're looking to supply budget 10Megabit servers, you should downscale the servers to ones with 200-250W PSU's.
You will also need to need a datacenter with low space and/or power costs... and nothing on the East Coast fits that bill.
-
10-01-2006, 09:07 AM #22Randy
- Join Date
- Aug 2006
- Location
- Ashburn VA, San Diego CA
- Posts
- 4,615
I would recommend going with AMD or Woodcrest processors instead. Those older Xeons are going to cook your cabinet!
Fast Serv Networks, LLC | AS29889 | DDOS Protected | Managed Cloud, Streaming, Dedicated Servers, Colo by-the-U
Since 2003 - Ashburn VA + San Diego CA Datacenters
-
10-01-2006, 09:16 AM #23Newbie
- Join Date
- Sep 2006
- Location
- New Jersey
- Posts
- 17
Hi,
Thank you everyone for your help.
Yeah, i never thought of going with a LV cpu. I know its a newer tech therefore would cost me more initially.
Also, go with a low powered server like 250wattt..etc Another great suggestion. Ive use Dell and never hand any problems with them, thats why i wanted to stick with dell. Any recommdations for other servers that has lower power and LV cpu that is reliable?
Yeah, MSV_AR is correct, the PSU is 325w. That didnt mean it always pushes the whole 325w.
btw, the more HD i put in, the more power it draws right? I guess its best to install 3x73gig then 5x36gig raid 5?
I thought 5x36gig would be much faster then 3x73gig. They both offer about same amount of storage.
bq_internet,
I think 10-15 servers is way too little 1u servers per cabinet. I think 30 minimum is ok. If the COLO is cool enough, i think it should be ok. Actually, my cabinet is right next to the cooling unit. I freeze my butt off working on my rack. Need a hooded sweatshirt. (C=
Thanx again everyone for your suggestions,
CalvinLast edited by xoopa; 10-01-2006 at 09:24 AM.
-
10-01-2006, 09:57 AM #24Web Hosting Guru
- Join Date
- Aug 2005
- Location
- PA
- Posts
- 324
A couple of observations:
1. I have a contract, right now, for 3x24A (actual) circuits in a Level3 facility in one rack, among other racks I have. That is 72A usable. And yes there is a big Liebert unit less than 30 feet away :-)
2. You really should get an electricity meter like the "Kill-A-Watt" meters (under $30) and measure how much a system uses when it is running but idle, what it uses when it is first turned on, and how much when it is busy doing something. Without that info, you are flying blind and just making guesses.reliable colocation ... Dedicated Servers | Dedicated Server VMs | FAST links to Vitelity.com and Conexiant.net
patrick@zill.net Cell +1.717.201.3366
-
10-01-2006, 12:19 PM #25WHT Addict
- Join Date
- Jun 2006
- Location
- Northern NJ
- Posts
- 112
Originally Posted by MfjpLast edited by ProRack; 10-01-2006 at 12:30 PM.
ProRack.com