Colocation and Data Centers Find data centers, server hardware, bandwidth providers, and techniques for colocation purposes. Get advice on colocation web hosting, review providers and offer suggestions on choosing colocation hosting services and the right datacenter. If your service is unavailable, please click here.
Forum Jump

Power consumption

Reply Post New Thread In Colocation and Data Centers Subscription
 
Send news tip View All Posts Thread Tools Search this Thread Display Modes
  #1  
Old 08-13-2006, 10:13 PM
supremehosting supremehosting is offline
Newbie
 
Join Date: Jul 2006
Posts: 13

Power consumption


Hi Guys, Im looking to get some feedback on the power consumption of our servers prior to installation.
We have a half rack with a power allocation of 8amps. Were planning to run dual core Optrons, obviously
we need to get the most from the space and were planning to use each rack space.

CPU: Dual Core Dual Opteron 270' (WITH 1MB of L2 Cache on each core.)
Chassis: 1U Supermicro
Memory: 4GB DDR
Storage: 4x 160GB WD SATA RAID5

Some of the servers will be dedicated to mail, others to DNS, actual web content, and others to database.

1) How much power do you think well require during the boot process for these servers.

2) For these servers to run close to capacity during peak hours, what do you think our power consumption will be per half rack.



Reply With Quote


Sponsored Links
  #2  
Old 08-14-2006, 01:15 AM
Mfjp Mfjp is offline
Web Hosting Master
 
Join Date: Nov 2002
Posts: 2,780
1) During the boot process, expect about 4amps to start up.
2) After boot up, each server of this type would draw about 2 to 2.5amps each. We have a similar system with 2 x 146GB 10K hdd, and they do about 2.2 when booted up.

__________________
http://Ethr.net jay@ethr.net
West Coast AT&T / Level3 / Savvis Bandwidth, Colocation, Dedicated Server, Managed IP Service, Hardware Load Balancing Service, Transport Service, 365 Main St, SFO / 200 Paul Ave, SFO / PAIX, PAO / Market Post Tower, 55 S. Market, SJC / 11 Great Oaks, Equinix, SJC

Reply With Quote
  #3  
Old 08-14-2006, 02:00 AM
supremehosting supremehosting is offline
Newbie
 
Join Date: Jul 2006
Posts: 13
Quote:
Originally Posted by Mfjp
1) During the boot process, expect about 4amps to start up.
2) After boot up, each server of this type would draw about 2 to 2.5amps each. We have a similar system with 2 x 146GB 10K hdd, and they do about 2.2 when booted up.
Have you had times where your available power was not enough to meet the 2.2amp requirement, if so how did the servers function.

Reply With Quote
Sponsored Links
  #4  
Old 08-14-2006, 03:12 AM
porcupine porcupine is offline
Web Hosting Master
 
Join Date: Dec 2001
Location: Toronto, Ontario, Canada
Posts: 5,553
Quote:
Originally Posted by supremehosting
Have you had times where your available power was not enough to meet the 2.2amp requirement, if so how did the servers function.
You'll simply blow the circuit breaker the servers are on, and the circuit will thus be shut down

__________________
Myles Loosley-Millman
Priority Colo Inc. - Affordable Colocation & Dedicated Servers.
admin@prioritycolo.com
http://www.prioritycolo.com

Reply With Quote
  #5  
Old 08-14-2006, 03:36 AM
supremehosting supremehosting is offline
Newbie
 
Join Date: Jul 2006
Posts: 13
Do the agree with the power requirements stated above.

Reply With Quote
  #6  
Old 08-14-2006, 03:43 AM
porcupine porcupine is offline
Web Hosting Master
 
Join Date: Dec 2001
Location: Toronto, Ontario, Canada
Posts: 5,553
Quote:
Originally Posted by supremehosting
Do the agree with the power requirements stated above.
Sustained power consumption of 2.5A for a quad (dual dual core) opteron 270 system with 4x sata drives is fairly reasonable. We have a customer with a cabinet full of 265's with 2 x 10k rpm raptor drives per system, they drive a *little* bit less then 2.5A/ea running, but are also fairly underutilized in terms of load.

__________________
Myles Loosley-Millman
Priority Colo Inc. - Affordable Colocation & Dedicated Servers.
admin@prioritycolo.com
http://www.prioritycolo.com

Reply With Quote
  #7  
Old 08-20-2006, 06:17 AM
RoryErickson RoryErickson is offline
Junior Guru
 
Join Date: Aug 2003
Location: Richmond, BC
Posts: 196
I would budget for at minimum 3A during bootup and ~2.5A during normal operation. That is, don't boot everything up at once if you're at your upper limit for the circuit.


A couple other items to remember however, and these are very important.

- Circuits don't really come as 8Amps, so you're likely going to be on a shared 15A or 20A circuit. That means you may or may not have someone else on the circuit who could be using more or less of their half allotment. Could work to your benefit or not.
- As an electrical code you never use your entire circuit, you use 80%. That means you don't have 8Amps available, you have 6.4Amps. Using more means your circuit is more prone to trip and is also more likely to fail pre-maturely--circuits over 80% sustained usage are prone to damage due to heat.

Reply With Quote
  #8  
Old 08-20-2006, 03:23 PM
timdorr timdorr is offline
Formerly orange-y
 
Join Date: Nov 2001
Location: Atlanta, GA
Posts: 632
Well, it also depends on how much usage you expect on those systems. We're doing 1.6A-2A on systems with very similar specs, just SCSI drives instead of SATA.

__________________
Former owner of A Small Orange
New owner of <COMING SOON>

Reply With Quote
  #9  
Old 08-23-2006, 02:38 AM
jimmy jimmy is offline
Newbie
 
Join Date: Jun 2001
Location: USA
Posts: 19
Quote:
Originally Posted by RoryErickson
- Circuits don't really come as 8Amps, so you're likely going to be on a shared 15A or 20A circuit. That means you may or may not have someone else on the circuit who could be using more or less of their half allotment. Could work to your benefit or not.
- As an electrical code you never use your entire circuit, you use 80%. That means you don't have 8 Amps available, you have 6.4Amps. Using more means your circuit is more prone to trip and is also more likely to fail pre-maturely--circuits over 80% sustained usage are prone to damage due to heat.

I second Rory's statement on the first part. However, on the second part, I am pretty sure that you can use the whole 8 amps for a 1/2 rack because a regular cabinet usually comes with 20 amp of power @ 120v. So a half rack will usually comes with 10 amp of power and at 80% utilization (fire code), that will give you a usable of 8 amps. (check with your provider to make sure weather the 8 amps is net or gross utilization)

If you have access to the server and can monitor the power usage before putting your server online, you can consider using kill a watt device as seen here: http://www.thinkgeek.com/homeoffice/gear/7657/
This will give you the amperage of your server utilization.

Reply With Quote
  #10  
Old 08-23-2006, 02:52 AM
RoryErickson RoryErickson is offline
Junior Guru
 
Join Date: Aug 2003
Location: Richmond, BC
Posts: 196
Quote:
Originally Posted by jimmy
I second Rory's statement on the first part. However, on the second part, I am pretty sure that you can use the whole 8 amps for a 1/2 rack because a regular cabinet usually comes with 20 amp of power @ 120v. So a half rack will usually comes with 10 amp of power and at 80% utilization (fire code), that will give you a usable of 8 amps. (check with your provider to make sure weather the 8 amps is net or gross utilization)

If you have access to the server and can monitor the power usage before putting your server online, you can consider using kill a watt device as seen here: http://www.thinkgeek.com/homeoffice/gear/7657/
This will give you the amperage of your server utilization.


It's a good point that they may have brought a 20A circuit to the full cabinet and have already calculated for the 80% utilization, I suppose the only way to know for sure would be to ask them.

If you want to know your usage at all times, you could even go for an APC Zero-U Metered Rack PDU. They're not 100% accurate, but would be close enough for your purposes.


- Rory

Reply With Quote
Reply

Related posts from TheWhir.com
Title Type Date Posted
Q&A: Jeffrey S. Klaus of Intel Data Center Manager Solutions Talks Power Efficiency Web Hosting News 2012-05-10 13:15:04
Web Host Bay Area Systems Launches Virtual Server Solutions Web Hosting News 2012-02-01 13:29:19
Modius OpenData Enterprise Integrates with Intel Data Center Manager Web Hosting News 2011-07-29 20:32:12
Data Center Operator Telx Uses FieldView Software to Measure Energy Consumption Web Hosting News 2011-07-11 20:38:41
Indian Leaders to Form Guidelines for Improving Data Center Energy Efficiency Web Hosting News 2011-06-20 15:59:38


Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes
Postbit Selector

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is Off
HTML code is Off

Forum Jump
Login:
Log in with your username and password
Username:
Password:



Forgot Password?
Advertisement:
Web Hosting News:



 

X

Welcome to WebHostingTalk.com

Create your username to jump into the discussion!

WebHostingTalk.com is the largest, most influentual web hosting community on the Internet. Join us by filling in the form below.


(4 digit year)

Already a member?