Datacenter cooling
To determine the cooling req. for a datacenter how many BTU are required per square feet?
Does under-floor (raised floor) requires cooling as well?
-
05-21-2004, 03:29 PM #2Hosting Specialist
- Join Date
- Dec 2003
- Location
- Boston, MA
- Posts
- 608
I know raised floor should be kept cool just becasue there hidden doesn't mean they are not important. Not sure of BTU I know right now my telco hotel houses 20TON Liebert's for 4,000 SQ FT.
Axcelx Technologies - James
Boston Colocation | Boston VPS
Massachusetts Server Colocation, Dedicated Servers & VPS
-
05-21-2004, 03:47 PM #3Web Hosting Master
- Join Date
- Oct 2001
- Location
- USA
- Posts
- 1,026
The under-floor/raised floor is where the cool air is pushed through by the HVAC (High Volume Air Conditioning). Then, the cool air will go up through small holes on the floor to cool the equipment above it. So, underneath the floor is actually cooler.
Reyner Natahamidjaja
:: Global IP Networks - Tier 3 Data Center and Managed IT Solutions
:: SSAE 16 SOC-2, PCI and HIPAA Compliant
:: https://gipnetworks.com
-
05-22-2004, 08:57 AM #4WHT Addict
- Join Date
- Feb 2004
- Posts
- 136
HVAC is actually a general term for "Heating-Ventalation-Air-Conditioning" not "High Volume"
20 Tons for 4,000 SqFt is actually somewhat undersized depending on the floorplan of the room. For the most part, you will want 250 BTU/sqFT for all of the areas that will contain equipment and less for aisles and open spaces.
-
05-22-2004, 09:56 AM #5Web Hosting Master
- Join Date
- Oct 2001
- Location
- USA
- Posts
- 1,026
Originally posted by DoubleD
HVAC is actually a general term for "Heating-Ventalation-Air-Conditioning" not "High Volume"
20 Tons for 4,000 SqFt is actually somewhat undersized depending on the floorplan of the room. For the most part, you will want 250 BTU/sqFT for all of the areas that will contain equipment and less for aisles and open spaces.
-
05-22-2004, 11:14 AM #6Web Hosting Master
- Join Date
- Dec 2001
- Location
- Houston Texas
- Posts
- 4,420
that is definately undersized depending on the application.
if you are housing a lot of servers you will need 20 tons per 1000 in a N+1redundant format of cooling.
so if you have 4000 sq ft of servers - you will need 80 tons + another 20 ton unit (if you units are 20 tons each) in case one goes down.
-
05-22-2004, 11:20 AM #7Hosting Specialist
- Join Date
- Dec 2003
- Location
- Boston, MA
- Posts
- 608
There 2 20Tons so 40TON's total and the SQ FT is 3,200 I belive. Is that good? I know the room is on the cold side and 75% full.
Axcelx Technologies - James
Boston Colocation | Boston VPS
Massachusetts Server Colocation, Dedicated Servers & VPS
-
05-22-2004, 11:26 AM #8Web Hosting Master
- Join Date
- Dec 2001
- Location
- Houston Texas
- Posts
- 4,420
Originally posted by Crucial
There 2 20Tons so 40TON's total and the SQ FT is 3,200 I belive. Is that good? I know the room is on the cold side and 75% full.
well - the question is - what if you lost a compressor? what if you lost a fan belt on the blower on one of them? what if you lost one of them due to electrical problems etc.
would the other one hold the temp till the first one is repaired?
will they hold the temp when you are full?
do you have electric capacity to add another one?
what percentage of the time are both compressors in the units running now? are they on 100% meaning you are at or near their total heat exchange limit already?
do you have outside coooling capacity to add another one?
those all need to be answerd,
-
05-22-2004, 11:31 AM #9Hosting Specialist
- Join Date
- Dec 2003
- Location
- Boston, MA
- Posts
- 608
Electric is not a problem, There not even at 50% on both 20TON and yes there is outside cooling capacity. I belive when the room is filled it will be around 50% on each. So if One fails I guess they other will be 100%.
Axcelx Technologies - James
Boston Colocation | Boston VPS
Massachusetts Server Colocation, Dedicated Servers & VPS
-
05-22-2004, 12:51 PM #10Temporarily Suspended
- Join Date
- Oct 2001
- Location
- Miami,FL
- Posts
- 616
Definitely raised floor datacenter is harder to maintain.
Thank you all for your usefull opinions.
-
05-22-2004, 10:08 PM #11Registered User
- Join Date
- Mar 2003
- Posts
- 1,584
40 tons, 20 tons or 80 tons of air ? they are all the right answer depending on how many servers you plan to place in the space and KVA load.
-
05-23-2004, 01:52 PM #12Aspiring Evangelist
- Join Date
- Jul 2001
- Location
- St. Louis
- Posts
- 379
N+1 means for each 20 ton unit you have a spare 20 ton unit. For example, we have ten CRAC (HVAC units designed for data centers - stands for Computer Room Air Condition) units and only five run at any one time. Therefore, if one of the units has a health issue, it can be taken off line and the alternate started to take its place.
Brad @ Xiolink
XIOLINK. Your data...always within reach.®
http://www.xiolink.com
1-877-4-XIOLINK [+01 314 621 5500]
-
05-23-2004, 10:00 PM #13Aspiring Evangelist
- Join Date
- Dec 2002
- Posts
- 376
I swear I thought N+1 mean Number+1, so you take the number of HVAC units you need and add one... It wouldnt really make sense to have a backup for EVERY unit, they arent ALL going to go down at the same time... or maybe at MOST two will go down (N+2)...? Maybe I'm wrong.
-
05-24-2004, 02:18 AM #14Backup Guru
- Join Date
- Feb 2002
- Location
- New York, NY
- Posts
- 4,618
f0urtyfive,
I believe you're right. What Brad is talking about is 2N reliability :-)Scott Burns, President
BQ Internet Corporation
Remote Rsync and FTP backup solutions
*** http://www.bqbackup.com/ ***
-
05-24-2004, 12:25 PM #15Web Hosting Master
- Join Date
- Apr 2001
- Location
- St. Louis, MO
- Posts
- 2,508
It depends on how your datacenter is set-up. For example, our datacenter is zoned so in each zone there is one unit with one backup. Each zone (5 zones in our Datacenter) has a primary unit and a backup.
Mike @ Xiolink.com
http://www.xiolink.com 1-877-4-XIOLINK
Advanced Managed Microsoft Hosting
"Your data... always within reach"
-
05-24-2004, 01:56 PM #16Web Hosting Master
- Join Date
- Dec 2001
- Location
- Houston Texas
- Posts
- 4,420
Originally posted by f0urtyfive
I swear I thought N+1 mean Number+1, so you take the number of HVAC units you need and add one... It wouldnt really make sense to have a backup for EVERY unit, they arent ALL going to go down at the same time... or maybe at MOST two will go down (N+2)...? Maybe I'm wrong.
not duplicate units for every unit. that wold become ungodly expensive.
also - all oyu need to do is replace the tonnage cooling in the room that is missed.
-
05-24-2004, 05:54 PM #17Junior Guru Wannabe
- Join Date
- Jun 2003
- Posts
- 71
People often overlook distribution when assessing HVAC redundancy. If your cabinet of expensive blade servers fries because the hvac unit at your end of the data center goes out, a standby unit at the other end of the data center that can't get the cooling to you does not offer much consolation. Call it what you will, your blades are still fried.
-
05-24-2004, 07:01 PM #18Web Hosting Master
- Join Date
- Dec 2001
- Location
- Houston Texas
- Posts
- 4,420
Originally posted by BandExch
People often overlook distribution when assessing HVAC redundancy. If your cabinet of expensive blade servers fries because the hvac unit at your end of the data center goes out, a standby unit at the other end of the data center that can't get the cooling to you does not offer much consolation. Call it what you will, your blades are still fried.
also one should have an ir temp guage so you can fine tune this in the dc. very helpful.
-
05-24-2004, 10:13 PM #19Web Hosting Master
- Join Date
- Apr 2001
- Location
- St. Louis, MO
- Posts
- 2,508
But doesn't an IR gauge only measure surface temp? Does not help with atmosphere.
Mike @ Xiolink.com
http://www.xiolink.com 1-877-4-XIOLINK
Advanced Managed Microsoft Hosting
"Your data... always within reach"
-
05-24-2004, 10:44 PM #20Web Hosting Master
- Join Date
- Dec 2001
- Location
- Houston Texas
- Posts
- 4,420
Originally posted by RackMy.com
But doesn't an IR gauge only measure surface temp? Does not help with atmosphere.
best tool I know of.
-
05-25-2004, 10:48 AM #21
<Drinking to much. Zeros were in the wrong place. >
Last edited by WII-Aaron; 05-25-2004 at 10:52 AM.