Colocation and Data Centers Find data centers, server hardware, bandwidth providers, and techniques for colocation purposes. Get advice on colocation web hosting, review providers and offer suggestions on choosing colocation hosting services and the right datacenter. If your service is unavailable, please click here.
Forum Jump

Datacenter cooling

Reply Post New Thread In Colocation and Data Centers Subscription
 
Send news tip View All Posts Thread Tools Search this Thread Display Modes
  #1  
Old 05-21-2004, 01:20 PM
DomiNET.net DomiNET.net is offline
Web Hosting Master
 
Join Date: Oct 2001
Location: Miami,FL
Posts: 592

Datacenter cooling


To determine the cooling req. for a datacenter how many BTU are required per square feet?

Does under-floor (raised floor) requires cooling as well?

__________________
Joman Sierra
http://www.dominet.net

Reply With Quote


Sponsored Links
  #2  
Old 05-21-2004, 03:29 PM
Crucial Crucial is offline
Boston Colocation and VPS
 
Join Date: Dec 2003
Location: Boston, MA
Posts: 592
I know raised floor should be kept cool just becasue there hidden doesn't mean they are not important. Not sure of BTU I know right now my telco hotel houses 20TON Liebert's for 4,000 SQ FT.

__________________
Axcelx Technolgies LLC
http://www.axcelx.com/
Boston Colocation + VPS Hosting
Boston, MA / Toll-Free 1-(877)-8AX-CELX

Reply With Quote
  #3  
Old 05-21-2004, 03:47 PM
rey rey is offline
Web Hosting Master
 
Join Date: Oct 2001
Location: USA
Posts: 1,020
The under-floor/raised floor is where the cool air is pushed through by the HVAC (High Volume Air Conditioning). Then, the cool air will go up through small holes on the floor to cool the equipment above it. So, underneath the floor is actually cooler.

__________________
Reyner Natahamidjaja | GIP Networks Inc
SSAE 16 SOC 1 Type II, PCI Compliant and 24/7 Dedicated Onsite Staff
Protecting Businesses Against Power Outage and Down Time


Reply With Quote
Sponsored Links
  #4  
Old 05-22-2004, 08:57 AM
DoubleD DoubleD is offline
WHT Addict
 
Join Date: Feb 2004
Posts: 136
HVAC is actually a general term for "Heating-Ventalation-Air-Conditioning" not "High Volume"


20 Tons for 4,000 SqFt is actually somewhat undersized depending on the floorplan of the room. For the most part, you will want 250 BTU/sqFT for all of the areas that will contain equipment and less for aisles and open spaces.

Reply With Quote
  #5  
Old 05-22-2004, 09:56 AM
rey rey is offline
Web Hosting Master
 
Join Date: Oct 2001
Location: USA
Posts: 1,020
Quote:
Originally posted by DoubleD
HVAC is actually a general term for "Heating-Ventalation-Air-Conditioning" not "High Volume"


20 Tons for 4,000 SqFt is actually somewhat undersized depending on the floorplan of the room. For the most part, you will want 250 BTU/sqFT for all of the areas that will contain equipment and less for aisles and open spaces.
Ah, that's right. HVAC is Heating, Ventilation & Air Conditioning and not High Volume. Thanks for the reminder DoubleD.

Reply With Quote
  #6  
Old 05-22-2004, 11:14 AM
sailor sailor is offline
cloud beats dedicated ;)
 
Join Date: Dec 2001
Location: Atlanta
Posts: 4,419
that is definately undersized depending on the application.

if you are housing a lot of servers you will need 20 tons per 1000 in a N+1redundant format of cooling.

so if you have 4000 sq ft of servers - you will need 80 tons + another 20 ton unit (if you units are 20 tons each) in case one goes down.

__________________
Experience the real cloud at GNAX
WWW.GNAX.NET
VMWare based cloud
Isn't it time to get off of dedicateds?

Reply With Quote
  #7  
Old 05-22-2004, 11:20 AM
Crucial Crucial is offline
Boston Colocation and VPS
 
Join Date: Dec 2003
Location: Boston, MA
Posts: 592
There 2 20Tons so 40TON's total and the SQ FT is 3,200 I belive. Is that good? I know the room is on the cold side and 75% full.

__________________
Axcelx Technolgies LLC
http://www.axcelx.com/
Boston Colocation + VPS Hosting
Boston, MA / Toll-Free 1-(877)-8AX-CELX

Reply With Quote
  #8  
Old 05-22-2004, 11:26 AM
sailor sailor is offline
cloud beats dedicated ;)
 
Join Date: Dec 2001
Location: Atlanta
Posts: 4,419
Quote:
Originally posted by Crucial
There 2 20Tons so 40TON's total and the SQ FT is 3,200 I belive. Is that good? I know the room is on the cold side and 75% full.

well - the question is - what if you lost a compressor? what if you lost a fan belt on the blower on one of them? what if you lost one of them due to electrical problems etc.

would the other one hold the temp till the first one is repaired?

will they hold the temp when you are full?

do you have electric capacity to add another one?

what percentage of the time are both compressors in the units running now? are they on 100% meaning you are at or near their total heat exchange limit already?

do you have outside coooling capacity to add another one?

those all need to be answerd,

__________________
Experience the real cloud at GNAX
WWW.GNAX.NET
VMWare based cloud
Isn't it time to get off of dedicateds?

Reply With Quote
  #9  
Old 05-22-2004, 11:31 AM
Crucial Crucial is offline
Boston Colocation and VPS
 
Join Date: Dec 2003
Location: Boston, MA
Posts: 592
Electric is not a problem, There not even at 50% on both 20TON and yes there is outside cooling capacity. I belive when the room is filled it will be around 50% on each. So if One fails I guess they other will be 100%.

__________________
Axcelx Technolgies LLC
http://www.axcelx.com/
Boston Colocation + VPS Hosting
Boston, MA / Toll-Free 1-(877)-8AX-CELX

Reply With Quote
  #10  
Old 05-22-2004, 12:51 PM
DomiNET.net DomiNET.net is offline
Web Hosting Master
 
Join Date: Oct 2001
Location: Miami,FL
Posts: 592
Definitely raised floor datacenter is harder to maintain.

Thank you all for your usefull opinions.

__________________
Joman Sierra
http://www.dominet.net

Reply With Quote
  #11  
Old 05-22-2004, 10:08 PM
music music is offline
Registered User
 
Join Date: Mar 2003
Posts: 1,584
40 tons, 20 tons or 80 tons of air ? they are all the right answer depending on how many servers you plan to place in the space and KVA load.

Reply With Quote
  #12  
Old 05-23-2004, 01:52 PM
Brad @ Xiolink Brad @ Xiolink is offline
Aspiring Evangelist
 
Join Date: Jul 2001
Location: St. Louis
Posts: 379
N+1 means for each 20 ton unit you have a spare 20 ton unit. For example, we have ten CRAC (HVAC units designed for data centers - stands for Computer Room Air Condition) units and only five run at any one time. Therefore, if one of the units has a health issue, it can be taken off line and the alternate started to take its place.

__________________
Brad @ Xiolink
XIOLINK. Your data...always within reach.®
http://www.xiolink.com
1-877-4-XIOLINK [+01 314 621 5500]

Reply With Quote
  #13  
Old 05-23-2004, 10:00 PM
f0urtyfive f0urtyfive is offline
Aspiring Evangelist
 
Join Date: Dec 2002
Posts: 376
I swear I thought N+1 mean Number+1, so you take the number of HVAC units you need and add one... It wouldnt really make sense to have a backup for EVERY unit, they arent ALL going to go down at the same time... or maybe at MOST two will go down (N+2)...? Maybe I'm wrong.

Reply With Quote
  #14  
Old 05-24-2004, 02:18 AM
bqinternet bqinternet is offline
Backup Guru
 
Join Date: Feb 2002
Location: New York, NY
Posts: 4,444
f0urtyfive,

I believe you're right. What Brad is talking about is 2N reliability :-)

__________________
Scott Burns, President
BQ Internet Corporation
Remote Rsync and FTP backup solutions
*** http://www.bqbackup.com/ ***

Reply With Quote
  #15  
Old 05-24-2004, 12:25 PM
RackMy.com RackMy.com is offline
Web Hosting Master
 
Join Date: Apr 2001
Location: St. Louis, MO
Posts: 2,508
It depends on how your datacenter is set-up. For example, our datacenter is zoned so in each zone there is one unit with one backup. Each zone (5 zones in our Datacenter) has a primary unit and a backup.

__________________
Mike @ Xiolink.com
http://www.xiolink.com 1-877-4-XIOLINK
Advanced Managed Microsoft Hosting
"Your data... always within reach"

Reply With Quote
Reply

Related posts from TheWhir.com
Title Type Date Posted
451 Research Publishes Report on Energy Efficiency Within Data Centers Web Hosting News 2012-10-17 15:53:09
Microsoft Updates Licensing, Offers Four Versions of Windows Server 2012 Web Hosting News 2012-07-06 10:31:48
Dell Expands VMware vCloud Data Center Services to Canada, Europe Web Hosting News 2012-06-15 15:48:31
Web Host Internet Solutions to Open Data Center in Johannesburg Web Hosting News 2011-09-29 17:45:45
Switch Datacenters Opens New 27,000 Square Foot Data Center in Amsterdam Web Hosting News 2011-08-24 20:37:02


Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes
Postbit Selector

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is Off
HTML code is Off

Forum Jump
Login:
Log in with your username and password
Username:
Password:



Forgot Password?
Advertisement:
Web Hosting News:



 

X

Welcome to WebHostingTalk.com

Create your username to jump into the discussion!

WebHostingTalk.com is the largest, most influentual web hosting community on the Internet. Join us by filling in the form below.


(4 digit year)

Already a member?