Metered/switched 30A 120V PDU without multiple banks of 20A circuits?
Is anyone aware of a metered or switched PDU that has everything on a single 30A 120V circuit, instead of the 2x 20A circuits that most of them come with?
[QuickPacket™] [AS46261]
Located in Ashburn, VA, Los Angeles, CA, Chicago, IL, and Manchester, UK
Since 2003 - 20+ Years! Dedicated Servers, Co-location, DDoS Filtering, Data Backup & More!0
-
01-08-2014, 09:59 PM #2WHT Addict
- Join Date
- May 2013
- Posts
- 157
I don't think that would meet UL since the output receptacles are not rated for 30A... So I doubt it exists.
0
-
01-08-2014, 10:19 PM #3Randy
- Join Date
- Aug 2006
- Location
- Ashburn VA, San Diego CA
- Posts
- 4,615
I'd recommend diving into a 20a / 208v circuit+PDU.
Fast Serv Networks, LLC | AS29889 | DDOS Protected | Managed Cloud, Streaming, Dedicated Servers, Colo by-the-U
Since 2003 - Ashburn VA + San Diego CA Datacenters0
-
01-08-2014, 10:33 PM #4Web Hosting Master
- Join Date
- Jun 2004
- Location
- Oregon
- Posts
- 1,315
Something like AP7932?
CNSERVERS.COM - Los Angeles, San Jose, Portland, Seattle, HongKong
AS40065 | In-House DDoS protection | BGP Network with 6T+ capacity
Zayo/HE/PCCW/Cogent/Telia/GTT/NTT/TATA/China Telecom/CN2/China Unicom/China Mobile
Colocation / DDOS Protection / High Bandwidth Server0
-
01-08-2014, 11:35 PM #5Web Hosting Master
- Join Date
- Oct 2000
- Posts
- 1,769
[QuickPacket™] [AS46261]
Located in Ashburn, VA, Los Angeles, CA, Chicago, IL, and Manchester, UK
Since 2003 - 20+ Years! Dedicated Servers, Co-location, DDoS Filtering, Data Backup & More!0
-
01-09-2014, 12:02 AM #6Web Hosting Evangelist
- Join Date
- Apr 2010
- Posts
- 493
0
-
01-09-2014, 12:07 AM #7Web Hosting Master
- Join Date
- Oct 2000
- Posts
- 1,769
No.
For example, the AP7932 (a 30A 120V PDU) has two banks of 12 power plugs, each on a 20A breaker. Other 30A 120V PDUs that we've seen are setup the same way.
We were hoping to find one that had a single 30A breaker for all of the plugs, rather than two 20A breakers with two separate banks.
208V is not readily available for this application.[QuickPacket™] [AS46261]
Located in Ashburn, VA, Los Angeles, CA, Chicago, IL, and Manchester, UK
Since 2003 - 20+ Years! Dedicated Servers, Co-location, DDoS Filtering, Data Backup & More!0
-
01-09-2014, 08:38 AM #8Web Hosting Master
- Join Date
- Aug 2003
- Location
- /dev/null
- Posts
- 2,132
Its not possible exactly due to what was said by Xeon852. It's a fire code breaking liability so no one will make one.
You MIGHT find something done (or custom order) by european companies with C13/C14 sockets but for 120V (although standard power @ Europe is 240V), then the sockets would be properly designed for 30A and thus would be able to suck all the power without melting down, and then would be certifiable/underwritable.0
-
01-09-2014, 10:00 AM #9Web Hosting Master
- Join Date
- Oct 2000
- Posts
- 1,769
[QuickPacket™] [AS46261]
Located in Ashburn, VA, Los Angeles, CA, Chicago, IL, and Manchester, UK
Since 2003 - 20+ Years! Dedicated Servers, Co-location, DDoS Filtering, Data Backup & More!0
-
01-09-2014, 10:38 AM #10Web Hosting Evangelist
- Join Date
- Apr 2010
- Posts
- 493
0
-
01-09-2014, 10:45 AM #11Web Hosting Master
- Join Date
- Aug 2003
- Location
- /dev/null
- Posts
- 2,132
C13 and C19 are 10A/16A @ 230V (2300W and 3680W respectively). Having a 30A@120V would be 3600W.
But yeah, 5-30r would be safer to find in the US.0
-
01-09-2014, 10:47 AM #12Junior Guru Wannabe
- Join Date
- Nov 2005
- Location
- Nassau, The Bahamas
- Posts
- 74
Secure Hosting | Premium Cloud & Dedicated hosting solutions since 2001
email: sales(at)securehost(dot)com • +1-242-502-8700 • 24/7 support by phone/helpdesk
Located in The Bahamas & Bermuda: Redundant Cooling, Power & Network, PCI DSS compliant, 7ms from USA
0
-
01-09-2014, 11:25 AM #13Web Hosting Evangelist
- Join Date
- Apr 2010
- Posts
- 493
The IEC connectors are odd ducks in that they are rated for up to 250v per IEC-60320. Pretty much the intent is to make a set of standard plugs/receptacles to go from whatever the local standard is to the IEC connector so that gear need not care what the local standard is aside from the odd 120/240v switch.
To describe them in watts is a bit disingenuous as that capacity changes dependent on local voltage. Amperage is limited independent of the voltage as that is mainly related to wire size. So while the connector and cable may be capable of supplying that many watts not at the stated voltage. As the OP states 208v or similar is not an option that means you need two or more banks with c13/c19 connectors to use 30a.0
-
01-10-2014, 05:15 AM #14Web Hosting Guru
- Join Date
- Jun 2011
- Location
- Portsmouth, UK
- Posts
- 327
As others have mentioned it's beyond the rating of the outputs so considered unsafe.
Why do you want it?
If your colo provider is giving you a 30A circuit then some kind of 30A to 2 x 16/20amp splitters and use the off the shelf APC stuff others have suggested.
Normally more breakers = more redundancy (a fault will trip less and thus turn off less devices) you have a higher fault current availabilityServerHouse | Est 2001 | 3x UK Data centres | Roof access, satcoms | High density | DR as standard
http://www.serverhouse.co.uk0
-
01-10-2014, 01:30 PM #15
Closed by OP's request.
Your one stop shop for decentralization
0
Similar Threads
-
Tripplite PDU's 110V 20A and 30A. Include SNMPweb card
By DatabaseByDesignLLC in forum Web Hosting HardwareReplies: 0Last Post: 01-07-2013, 05:47 PM -
FS: AP7902 2U, 30A, 16 port, 120v Switched & Metered PDU(s)
By RyanD in forum Web Hosting HardwareReplies: 0Last Post: 09-22-2010, 05:05 PM -
APC AP7932 SWITCHED PDU 120V 30A NEW
By inteltechs in forum Web Hosting HardwareReplies: 0Last Post: 07-14-2010, 08:49 PM -
APC AP7930 Rack PDU, Switched, Zero U, 20A, 120V
By hilsiddiqui in forum Dedicated ServerReplies: 6Last Post: 05-20-2010, 12:51 PM -
APC Rack PDU, Switched, 1U, 20A, 120V, (8)5-20
By ioZoom in forum Other Web Hosting Related OffersReplies: 0Last Post: 03-27-2007, 07:06 PM