    Quote Originally Posted by nightmarecolo4 View Post
    I have just lost my biggest client
    Just curious. How much money per month was your biggest client paying for hosting?
      0 Not allowed!

  2. #77
    Do you people who are screaming for an ETA really not understand how this stuff works? Really? You're IT people, right?
      0 Not allowed!

  3. #78
    Join Date
    Mar 2006
    Location
    Reston, VA
    Posts
    3,132
    Quote Originally Posted by nightmarecolo4 View Post
    simply by-pass the ATS and power the UPS with generator power (re-fuel gen as needed until a good solution is in place). Join the lines up inside the ATS. Should have been done already- Its going to take a long time to wire another ATS
    Thats not going to happen, the whole point of the ATS is to transfer the power load from generator pathway to utility. You just can't by pass it without taking everything back down again.

    Of course.. unless you are a tier4 datacenter with 2n+1/2
      0 Not allowed!

  4. #79

    same here - site down!

    Site's been down all day... This is unacceptable!!!!

    Thousands of dollars have been lost by many of us I'm sure.
      0 Not allowed!

  5. #80
    Join Date
    Jun 2002
    Location
    Houston, TX
    Posts
    119
    Yeah it is hard to understand how UPS/generators haven't kicked in for this situation.
      0 Not allowed!

  6. #81

    Unhappy 500

    Quote Originally Posted by neumannu47 View Post
    Just curious. How much money per month was your biggest client paying for hosting?
    $500 per month on a dedicated server to them that we managed
      0 Not allowed!

  7. #82
    I'm not really smart with all this stuff but...yeah...I was thinking all this time, don't they at least have a generator as backup?
      0 Not allowed!

  8. #83
    Join Date
    Dec 2002
    Location
    USA
    Posts
    51
    I am questioning their tagline of "Unrivaled Support"!!!! Lack of eta makes me question that.
      0 Not allowed!

  9. #84
    I don't' remember being offered any A/B anything by my hosting company rimuhosting, or else I would've opted for it had I known it would prevent this 3+ hours of downtime. We need this problem fixed 3 hours ago.
      0 Not allowed!

  10. #85
    As a customer of one of the webhosts on here I can understand your frustration. I have called my host about 10 times trying to get information and sent emails. However in the same respect as it has been said above, cant always give a timeframe because sometimes ya just dont know.
      0 Not allowed!

  11. #86
    Join Date
    Aug 2007
    Location
    Lincoln, UK
    Posts
    439
    Quote Originally Posted by jumpoint View Post
    This may be a dumb questionn, but if you were to simply go and swap your cables from A to B side, would that work? Or is that something that would have to have been pre-configured.
    Assuming that the A and B sides have the same capacity (why would you pay to install extra capacity on the B side until there is customer demand for it, you are just incurring CapEx by buying expensive equipment and OpEx by lowering your efficiency) then you would still need to either run new whips from each rack to the B-side PDUs or re-wire the A-side PDUs into the B-side bus. Neither of those is a quick or easy solution.
      0 Not allowed!

  12. #87
    Join Date
    May 2009
    Location
    Midworld
    Posts
    1,814
    Quite epic now, and frustrating.
      0 Not allowed!

  13. #88
    Quote Originally Posted by httpEasy View Post
    Quite epic now, and frustrating.
    Epic ..... Now thats a description LOL
      0 Not allowed!

  14. #89
    I already threatened to quit my webhost for this. He's said he's quitting colo4 now though so we shall see.
      0 Not allowed!

  15. #90
    This is the real world people. When non-standard things happen you try your hardest and you're done when its done. If you can't estimate how long it's going to take you can't.

    If they underestimate it everyone will be complaining that they were lied to and how unjust that is. If they overestimate everyone will complain about how long it is still going to take from the start.

    It being unacceptable and such do not change the reality of the matter. They have quite a bit of redundancy in place but in the end you cannot protect yourself from everything.

    And yes my company is affected too, taking my anger out here won't bring it back.

    As for all the 'Why have the backup generators not kicked in???' reading the entire thread may be more advised than flooding it with the same questions over and over.

    In short these things happen, deal with it and rely on your datacenter or switch occupations.
      0 Not allowed!

Page 6 of 24 FirstFirst ... 345678916 ... LastLast

Similar Threads

  1. Speakers and entrance fees :(
    By Mike - Limestone in forum Web Hosting Lounge
    Replies: 10
    Last Post: 07-21-2009, 10:32 AM
  2. Any Suggestions (entrance Music) ?
    By Darktwist in forum Web Hosting Lounge
    Replies: 8
    Last Post: 08-22-2005, 10:34 AM
  3. Hater-aid At The Front Entrance Of The Forums
    By s2shost in forum Web Hosting Lounge
    Replies: 6
    Last Post: 06-08-2004, 09:55 PM
  4. College Entrance Exam for Student Athletes
    By The Dude in forum Web Hosting Lounge
    Replies: 6
    Last Post: 01-21-2003, 12:07 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •