Major spike in Electrical Bill - Strategies to reduce utility demand usage & usage?
Hey All,
Got a bit of a surprise today and curious to hear your thoughts.
We operate a new data center in a very expensive state in terms of energy costs (we are in the northeast). Starting this business has been a great learning experience, lots of trial and error. I do not profess to be an expert on the electrical engineering side (but look forward to learning) so please excuse my lack of knowledge. In the last 4 billing cycles (4 months), the billing was based on estimated readings, hovering around 9,000 KWh usage during the winter months. This translated to roughly $2k monthly all said and done. Our generation service charge was on a variable rate of $.079900, from a third party energy supplier.
Over the last four months, we had a false sense of security in our cost expectations, and projections of our power cost and PUE based on "estimated meter reads". We were probably a bit more liberal with heating because of it. Unfortunately, our heat is electrical, (no natural gas line coming in, costs $40,000 to implement from the street.) We have brought in new customers, but I do not believe their hardware configurations are accounting for the majority of the energy consumption and cost (yet).
After four months of "estimated meter reading" (which I confess I thought was standard meter reading process), February came, where an actual read of 26 days happened. Bottom line, our usage (and costs) jumped more than 4 times from 9,000 KWH usage to 40,000KWH usage based on the actual read of the meter (first time in 4 months). To make matters worse, our variable price by the energy supplier jumped to .109 cents per KWH. (We have already submitted a requested to switch to a fixed rate of $.086) Lastly, our demand charge went from 45 KW to 73KW. I disputed the bill with the power company, but after some more research I may have to accept the bill.
We have certainly learned our lesson and power monitoring and efficiency is a major part of focus now.
So we are going to focus on reducing power consumption. I wanted to know what protocols and controls some of you implemented for environmental control. Our data center has 24/7 access, and in the winter months we do not want our customers to be cold. I was wondering if anyone has implemented some automatic environmental controls for those times a client may show up at 3:00am. (I'm thinking when they enter the facility with their rd card, there is some trigger to turn on the heat, otherwise everything remains off until there is someone actually in the facility.
Additionally, we certainly could do better with motion active lighting etc. We will have to accept the consumption of our 40 ton Liebert CRAC unit and dry coolers of course.
I am sure all data center owners went through a similar growing pain in the early months of their business and systematically off the excess energy usage and waste. Any further advice, monitoring software/controls or general strategies as we re-structure our energy approach is greatly appreciated. Thank you in advance.
Rob
-
03-07-2011, 11:10 PM #2Web Hosting Master
- Join Date
- Nov 2009
- Location
- Cincinnati
- Posts
- 1,585
Do you utilize the colder temperatures of the northern areas in the winter to reduce power consumption by using a 2 phase heat exchanger?
Also, I would push out a bulletin asking customers to set servers to power save mode vs performance. There is no reason what so ever to have a server run max out if its doing nothing, intel cpus have great power scaling and it should be utilized. AMD isn't far behind.
Your lighting is at most 2% of the monthly power bill.'Ripcord'ing is the only way!
-
03-07-2011, 11:17 PM #3Master of the Truth
- Join Date
- Mar 2006
- Location
- Reston, VA
- Posts
- 3,131
What cooling equipment do you use?
You really should be using a system like powerlogic to monitor _everything_ related to power so you know exactly what your PUE is and where your power bill is going, also a good audit against the power company etc.Yellow Fiber Networks
http://www.yellowfiber.net : Managed Solutions - Colocation - Network Services IPv4/IPv6
Ashburn/Denver/NYC/Dallas/Chicago Markets Served zak@yellowfiber.net
-
03-07-2011, 11:34 PM #4Web Hosting Master
- Join Date
- Aug 2007
- Location
- L.A., CA
- Posts
- 3,710
You could try to recirculate air from the hot rows into the plenum and use some of that to warm the office area (if feasible, I don't know your floorplan).
Though, I don't think keeping your office area warm is going to be that large of a cost... Keeping it "acceptable" at around 65-68F is probably fine, you don't have to heat it to 72F+.
Is your Liebert at any point ever shutting down the compressor or do you have it set so low that it runs 24/7 as it will never reach the set point temperature?
What caused your demand charge to jump so high?Last edited by ItsChrisG; 03-07-2011 at 11:40 PM.
EasyDCIM.com - DataCenter Infrastructure Management - HELLO DEDICATED SERVER & COLO PROVIDERS! - Reach Me: chris@easydcim.com
Bandwidth Billing | Inventory & Asset Management | Server Control
Order Forms | Reboots | IPMI Control | IP Management | Reverse&Forward DNS | Rack Management
-
03-07-2011, 11:40 PM #5Disabled
- Join Date
- Aug 2009
- Posts
- 39
Thanks.
Thanks for the reply's everyone.
Just to answer a couple of questions. We use a 40 ton Liebert CRAC unit + a 3 fan dry cooler outside.
I will check into power logic right now. And as for the 2 phase heat exchanger, this is the first time I have heard of that. Visbits could you explain a bit more about this?
We have not yet gotten too creative in harnessing the seasons of the north east, so I'm very happy to be having this discussion.
Lastly, good idea about requesting the clients to use power save modes. Additionally, very much like the idea of channeling the hot air into the office spaces, our floorplan would work well with this.
Thanks again guys.
-
03-07-2011, 11:43 PM #6Web Hosting Master
- Join Date
- Aug 2007
- Location
- L.A., CA
- Posts
- 3,710
I don't think telling your clients to set their equipment to power save mode is going to fly.
Most people are anal about having their machines at max performance 24/7 and they will argue that they are paying for the power, so they should be able to use it.
You may want to look at what you are charging these customers for their colocation... you may have underpriced things before you knew what your actual costs were going to be like per 1Amp of their usage...EasyDCIM.com - DataCenter Infrastructure Management - HELLO DEDICATED SERVER & COLO PROVIDERS! - Reach Me: chris@easydcim.com
Bandwidth Billing | Inventory & Asset Management | Server Control
Order Forms | Reboots | IPMI Control | IP Management | Reverse&Forward DNS | Rack Management
-
03-07-2011, 11:51 PM #7Web Hosting Evangelist
- Join Date
- Nov 2001
- Posts
- 489
To make matters worse, our variable price by the energy supplier jumped to .109 cents per KWH. (We have already submitted a requested to switch to a fixed rate of $.086)
-Tom
-
03-08-2011, 12:21 AM #8Web Hosting Master
- Join Date
- Nov 2009
- Location
- Cincinnati
- Posts
- 1,585
I'm not for sure on a manufacture or model but the 2 data center facility we are using here in cincinnati use a 2 phase exchanger in the winter, they are using a ethylene glycol cooling system that is chilled to 58F, well if its 50F or less outside it would be wise to utilize it.
The system is just a bunch of radiators and fans, rather simple device.
So all those days its less than 50F outside your AC units wouldn't be running, that's what 200 amps your not using?'Ripcord'ing is the only way!
-
03-08-2011, 12:51 AM #9Disabled
- Join Date
- Aug 2009
- Posts
- 39
Thanks again for the replys all. You guys are great.
Curious about room for negotiation with energy suppliers, particularly as a data center that relatively speaking will consume more energy than other industries. Anyone have any luck?
-
03-08-2011, 12:54 AM #10Temporarily Suspended
- Join Date
- Jan 2010
- Posts
- 652
(I'm thinking when they enter the facility with their rd card, there is some trigger to turn on the heat,
We will have to accept the consumption of our 40 ton Liebert CRAC unit and dry coolers of course.
Additionally, investigate 'free cooling' opportunities such as mentioned above (glycol heat exchangers or air-side economizers)
Also, next time, do NOT get a CRAC unit with the compressor in the air handler.
-
03-08-2011, 04:33 AM #11Web Hosting Master
- Join Date
- Jun 2001
- Location
- Denver, CO
- Posts
- 3,302
Some random thoughts:
- You have a single 40 ton CRAC unit, on a 3 fan dry cooler? That setup alone is probably pulling down about 45-50 amps on 480v 3 phase, roughly 37KW / 26000kWH/mo.
- What are your set points?
- What is the size of your critical load? I'm guessing pretty small, probably around 35-40KW?
- I wonder why you went with a single 40 ton unit, and not something more aptly sized, like two 20 ton units, as this would have also gotten you N+1 and cost much less to operate.
- Are you doing any sort of hot aisle/cold aisle containment?
- If your winter rates are $.10/kWH, I shudder to think what it's going to cost you in the summer months.
- You might want to give these folks a call: http://www.enabledenergy.net/Jay Sudowski // Handy Networks LLC // Co-Founder & CTO
AS30475 - Level(3), HE, Telia, XO and Cogent. Noction optimized network.
Offering Dedicated Server and Colocation Hosting from our SSAE 16 SOC 2, Type 2 Certified Data Center.
Current specials here. Check them out.
-
03-08-2011, 04:49 AM #12Managed Service Provider
- Join Date
- Feb 2004
- Location
- Atlanta, GA
- Posts
- 5,662
-
03-15-2011, 01:43 PM #13Web Hosting Guru
- Join Date
- Nov 2009
- Location
- Reston
- Posts
- 305
-Older UPS systems can add quite a bit of power consumption.
-Cold aisle containment systems may also help you to maximize the usage on your CRAC units, allowing you to turn them down a few notches. It's also arguable to use hot aisle containment and I don't have the hard facts as to which is more efficient.
-If you are operating a smaller DC, a few thousand sf, you could look into get a timer / motion sensor set on your lights to shut off if no one is on the floor.
Just some simple suggestions. Cooling does normally account for close to 30% of your monthly cooling bill, so it is a large factor to consider. UPS can be an expensive component and may require some downtime depending on how the infrastructure is configured.Dan Buyer
InfoRelay - Connected, Protected, Perfected.
Equinix LAX & DC, One Wilshire, Wilshire Annex, MPT, VE, 1275K, Reston Exchange, Reston Equinix, 60 Hudson, NYC, and Chicago
www.inforelay.com
Similar Threads
-
need to reduce bandwidth usage
By riquelme in forum Dedicated ServerReplies: 17Last Post: 01-23-2008, 06:04 PM -
Please help me to reduce memory usage for httpsd&httpd
By Kirill78 in forum Hosting Security and TechnologyReplies: 2Last Post: 01-06-2006, 02:14 PM -
How can I reduce my bandwidth usage
By Phach in forum Web HostingReplies: 12Last Post: 01-20-2005, 03:03 AM -
Is this CPU Usage spike normal?
By Collaziano in forum Dedicated ServerReplies: 4Last Post: 04-05-2004, 03:34 PM -
raq server and memory usage spike---->crash
By kickster in forum Dedicated ServerReplies: 2Last Post: 04-30-2002, 09:48 AM