hosted by liquidweb


Go Back   Web Hosting Talk : Web Hosting Main Forums : Colocation and Data Centers : Peer 1 Seattle (Westin) Planned power outage. What?
Reply

Colocation and Data Centers Find data centers, server hardware, bandwidth providers, and techniques for colocation purposes. Get advice on colocation web hosting, review providers and offer suggestions on choosing colocation hosting services and the right datacenter. If your service is unavailable, please click here.
Forum Jump

Peer 1 Seattle (Westin) Planned power outage. What?

Reply Post New Thread In Colocation and Data Centers Subscription
 
Send news tip View All Posts Thread Tools Search this Thread Display Modes
  #1  
Old 03-01-2011, 11:36 PM
funkee funkee is offline
Junior Guru Wannabe
 
Join Date: Feb 2001
Posts: 55

Peer 1 Seattle (Westin) Planned power outage. What?


So I got an email from peer 1 detailing a 30 minute planned power outage on Mar 16th " to replace the transformer and bypass panel feeding our Seattle 7th Floor Data Center."

"There is also a potential for short periods of power loss during a 90 minute testing phase that follows the 30 minute shut down."

I have never heard of intentionally powering down a data centre. Is this common? I would think that in a properly designed data centre one would have multiple power feeds and have the ability to work on them separately without a service interruption.

They go on to say "Due to the impact this will cause we are offering you the option to have a Data Center Technician power off their equipment prior to the 30 minute shut down window. You can then choose to have your equipment powered on after the 30 minute shut down or wait until the 90 minute testing is complete."

Reply With Quote


Sponsored Links
  #2  
Old 03-01-2011, 11:59 PM
andrewinet andrewinet is offline
Junior Guru Wannabe
 
Join Date: Jan 2011
Posts: 71
Is it common, sure. It's common to power everything down on one feed, once every 3 to 5 years, for inspection and cleaning purposes at the very minimum. That's why some facilities operate dual independent A/B feeds with shared-nothing architecture - if you need to take one down, the other one remains perfectly viable.

Reply With Quote
  #3  
Old 03-02-2011, 12:19 AM
Dougy Dougy is online now
Rockin' the beer gut
 
Join Date: May 2006
Location: NJ, USA
Posts: 6,032
Quote:
Originally Posted by funkee View Post
So I got an email from peer 1 detailing a 30 minute planned power outage on Mar 16th " to replace the transformer and bypass panel feeding our Seattle 7th Floor Data Center."

"There is also a potential for short periods of power loss during a 90 minute testing phase that follows the 30 minute shut down."

I have never heard of intentionally powering down a data centre. Is this common? I would think that in a properly designed data centre one would have multiple power feeds and have the ability to work on them separately without a service interruption.

They go on to say "Due to the impact this will cause we are offering you the option to have a Data Center Technician power off their equipment prior to the 30 minute shut down window. You can then choose to have your equipment powered on after the 30 minute shut down or wait until the 90 minute testing is complete."
I usually see a full shutdown with financial data centers since they are dead to the world on weekends.. but not normal datacenters..

__________________
simplywww: directadmin and cpanel hosting that will rock your socks
coming very soon: Cheapest Comodo SSL certificates on the market

Need some work done in a datacenter in the NYC area? NYC Remote Hands can do it.

Reply With Quote
Sponsored Links
  #4  
Old 03-02-2011, 01:33 AM
pubcrawler pubcrawler is offline
Aspiring Evangelist
 
Join Date: Aug 2007
Posts: 351
Sounds like 2011 is going to be the year of electric issues in data centers. Both intentional and unintentional.

Reply With Quote
  #5  
Old 03-02-2011, 01:50 AM
CGotzmann CGotzmann is offline
|=|*LL* * *m Chr**
 
Join Date: Aug 2007
Location: DOWNTOWN LOS ANGELES
Posts: 2,596
Quote:
Originally Posted by funkee View Post
So I got an email from peer 1 detailing a 30 minute planned power outage on Mar 16th " to replace the transformer and bypass panel feeding our Seattle 7th Floor Data Center."

"There is also a potential for short periods of power loss during a 90 minute testing phase that follows the 30 minute shut down."

I have never heard of intentionally powering down a data centre. Is this common? I would think that in a properly designed data centre one would have multiple power feeds and have the ability to work on them separately without a service interruption.

They go on to say "Due to the impact this will cause we are offering you the option to have a Data Center Technician power off their equipment prior to the 30 minute shut down window. You can then choose to have your equipment powered on after the 30 minute shut down or wait until the 90 minute testing is complete."
Uh, unless you yourself are also running A+B circuits with redundant power supplies in your servers, you are more than likely plugged into ONE UPS, ONE ATS, ONE BREAKER PANEL, etc.
If any of those need maintenance or experience an outage, there is absolutely nothing you can do to avoid downtime. Unless your datacenter specifically sold you some other type of agreement, then thats how it most likely is.

__________________
QuadraNet.com™ - Enterprise Dedicated Servers, Cloud Hosting, and Colocation
Focused on automation, accessibility, and scalability. Datacenters in Los Angeles Dallas Miami
Features Include: Private Network, SSL VPN Passthru, KVM over IP, Remote Reboot, Remote OS Reload
Read our BLOG! http://blog.quadranet.com Try our Asian Optimized Network in LA!

Reply With Quote
  #6  
Old 03-02-2011, 03:16 AM
funkee funkee is offline
Junior Guru Wannabe
 
Join Date: Feb 2001
Posts: 55
Quote:
Originally Posted by CGotzmann View Post
Uh, unless you yourself are also running A+B circuits with redundant power supplies in your servers, you are more than likely plugged into ONE UPS, ONE ATS, ONE BREAKER PANEL, etc.
If any of those need maintenance or experience an outage, there is absolutely nothing you can do to avoid downtime. Unless your datacenter specifically sold you some other type of agreement, then thats how it most likely is.
Shouldn't the UPS sit between all that stuff and your servers? If equipment upstream from the ups needs servicing then that shouldn't be a problem and if the UPS needs servicing it can be bypassed temporarily.

I've had space in three data centres for almost 10 years and have had notifications of all kinds of electrical work but it has always been not service impacting.

FYI Luckily I don't actually have any equipment @ peer1 so this is just a philosophical discussion.

Reply With Quote
  #7  
Old 03-02-2011, 03:31 AM
pubcrawler pubcrawler is offline
Aspiring Evangelist
 
Join Date: Aug 2007
Posts: 351
@funkee

I agree with your assessment and share your opinion.

I find it shocking how non-redundant an ever growing number of data centers are in reality (not in their self promotion marketing materials).

When people come down on cheap facilities and DIY non traditional data centers it's for things like described - single homed non redundant power.

30 minute shutdown + 90 minutes of testing = 2 HOURS of downtime.

That would take that facilities uptime for the entire year (absent any other outages) down to 99.97% roughly.

Peer1 boasts a 100% uptime SLA seemingly standard. Obviously, this work window is some sort of exemption in the legalese I suspect.

There are going to be a number of folks who never got the email about this work. A number of servers that don't restart right or which services don't start and config issues. There always are

FYI: I don't have gear with Peer1 and won't any time in the future.

Reply With Quote
  #8  
Old 03-02-2011, 03:31 AM
CGotzmann CGotzmann is offline
|=|*LL* * *m Chr**
 
Join Date: Aug 2007
Location: DOWNTOWN LOS ANGELES
Posts: 2,596
Quote:
Originally Posted by funkee View Post
Shouldn't the UPS sit between all that stuff and your servers? If equipment upstream from the ups needs servicing then that shouldn't be a problem and if the UPS needs servicing it can be bypassed temporarily.

I've had space in three data centres for almost 10 years and have had notifications of all kinds of electrical work but it has always been not service impacting.

FYI Luckily I don't actually have any equipment @ peer1 so this is just a philosophical discussion.
The UPS can power equipment for at maximum between 5-10 minutes depending on load levels. UPS's are just used for the temporary interruption of power from utility feed drop to generator spinup/power up.
Though they said transformer so they could possibly bypass over to generator power while they perform the maintenance on the transformer... but then they also mentioned the bypass panel, which could mean the ATS bypass panel, thus rendering the ability to actually transfer between utility and generator power, null.

It happens... sometimes things just have to go down or break on their own, no matter how redundant

__________________
QuadraNet.com™ - Enterprise Dedicated Servers, Cloud Hosting, and Colocation
Focused on automation, accessibility, and scalability. Datacenters in Los Angeles Dallas Miami
Features Include: Private Network, SSL VPN Passthru, KVM over IP, Remote Reboot, Remote OS Reload
Read our BLOG! http://blog.quadranet.com Try our Asian Optimized Network in LA!

Reply With Quote
  #9  
Old 03-02-2011, 03:48 AM
andrewinet andrewinet is offline
Junior Guru Wannabe
 
Join Date: Jan 2011
Posts: 71
Quote:
Originally Posted by funkee View Post
Shouldn't the UPS sit between all that stuff and your servers?
Not necessarily. There are stepdown transformers ahead of the UPS at some point, but the UPS output power usually runs through another transformer, because it's usually 3ph 480v and needs to step down to something usable by customers, like 3ph 208v. As they mentioned the bypass panel (presumably the UPS full-wrap bypass), I'm guessing the transformer they're referring to is the output transformer.

Quote:
Originally Posted by pubcrawler
When people come down on cheap facilities and DIY non traditional data centers it's for things like described - single homed non redundant power.
Ok but there's nothing wrong with a facility owner choosing to operate this way, and there's nothing wrong with a customer buying this service as-is, so long as the facility is honest and forthright about their capabilities. Some people are ok paying double for A and B feeds, usually totaling some $750/mo for dual 110v 20a circuits. Others want to pay what this actually costs the facility, typically a bit under $200/mo for a single feed, and are willing to forego the increased reliability along with the price. Multiply that over 10 or 20 cabinets.. the difference is a Lexus and a big house.

Reply With Quote
  #10  
Old 03-02-2011, 04:14 AM
IRCCo Jeff IRCCo Jeff is online now
CISSP, CISA
 
Join Date: Aug 2002
Location: Los Angeles, CA
Posts: 5,036
We were down for about 45 minutes in 2009 when Peer1 lost an entire row of cabinets in Los Angeles. They didn't know about it until we opened a ticket and someone went to look at it.

At least this time you have warning

__________________
Black Lotus - Carrier Neutral Datacenter & DDoS Mitigation Solutions
Access to over 200 carriers | 60A per cabinet | Local, remote, proxy, and BGP GRE DDoS protection

>>> Take a virtual tour of the Black Lotus LA2 datacenter, our own Tier III facility


Reply With Quote
  #11  
Old 03-02-2011, 04:38 AM
appliedops appliedops is offline
NetOps Ninja
 
Join Date: Jan 2005
Location: San Francisco/Hot Springs
Posts: 984
Quote:
Originally Posted by funkee View Post
I have never heard of intentionally powering down a data centre. Is this common? I would think that in a properly designed data centre one would have multiple power feeds and have the ability to work on them separately without a service interruption.
It happens quite a bit, its called "maintenance"
Seriously though, everything has to turn off sometimes, one way or another.

__________________
AppliedOperations - Premium Service
Bandwidth | Colocation | Hosting | Managed Services | Consulting
www.appliedops.net

Reply With Quote
  #12  
Old 03-02-2011, 05:24 AM
Rob T Rob T is offline
Web Hosting Master
 
Join Date: Jun 2003
Location: Las Vegas, NV
Posts: 590
There are certainly issues where power has to be disabled in order to perform upgrades, maintenance, or to make other changes. Based on the info provided by Peer1 in the email you shared, I'd guess that they may be doing maintenance on a low-voltage distribution transformer that feeds a distribution panel and it's related bypass - because those are downstream of any UPS gear in most cases, it's not typically possible to perform maintenance on that type of gear without taking the power offline. That's just a guess, but it would make sense as to why they can't maintain power during the maintenance.

Even in facilities that offer a true A/B power infrastructure, in my experience many of the customers in the facility either won't elect to pay for A/B power, and those that do in many cases make implementation errors that result in a partial outage if one of their power feeds does go down. We typically recommend that our customers utilize a rack PDU that has a built-in ATS to make sure that they are truly A/B redundant, that way they don't have to use servers and other equipment with dual PSU's in order to maintain A/B power redundancy at the equipment level.

__________________
Rob Tyree
Versaweb - Cloud and Dedicated Server Hosting
Fiberhub - SAS70 Type-II Colocation in Las Vegas and Seattle

Reply With Quote
  #13  
Old 03-02-2011, 05:36 AM
andrewinet andrewinet is offline
Junior Guru Wannabe
 
Join Date: Jan 2011
Posts: 71
To the original poster, I just noticed the "bad design" tag that you placed on this thread. You did know you were buying a single feed, and that invariably you'd have no redundancy *when*, not *if* they needed to take the power down for maintenance, right?

Reply With Quote
  #14  
Old 03-02-2011, 10:10 AM
leeware leeware is offline
Aspiring Evangelist
 
Join Date: Nov 2004
Location: Chicago
Posts: 413
I was going to reply to this after he first posted but it is another example of people (a) not understanding what they are buying and (b) having completely unrealistic expectations of services when it comes to the prices they are paying.

As others have alluded to here, in a shared nothing environment where the cost would make most users lurking on WHT puke these kinds of issues are less common. However, for just about any service this is affordable to people buying services offered here, there is a good chance these things will happen from time-to-time. This doesn't mean that a facility is poorly design. Providers can spend endless amounts of money trying to make sure everything is always available. However, the fundamental problem is twofold:

(1) Most customers are not going to want to pay the higher costs for such reliability ($$$-$,$$$/month).


(2) It seems rather pointless to complain about a providers lack of redundancy especially when customers demand services for pennies and don't invest their savings into building redundancy into their applications or services.


Therefore, the approach most end-users take is: Find least expensive provider that offers the highest levels of reliability and host my single (point-of-failure) application with said provider. When something goes wrong, point the finger at the provider.

It would be helpful if these users remembered the motto:

Two is one and one is none.

__________________
Lee Evans, Owner/Operator
LeeWare Development
Linux Dedicated Server Grids
http://www.leeware.com

Reply With Quote
  #15  
Old 03-02-2011, 11:25 AM
RSanders RSanders is offline
Web Hosting Master
 
Join Date: Feb 2003
Location: Detroit
Posts: 795
Sure, 440V UPS to transformer to service panel. This sounds like a typical setup and the only way to service it past the UPS point is to shutdown.

This is why redundant power paths can be important. You should be able to order a second power circuit off of a independent UPS and transformer, at a premium price. This can not be built into a single circuit feed and is much more expensive to provide.

Reply With Quote
Reply

Similar Threads
Thread Thread Starter Forum Replies Last Post
Transfer from Westin Seattle -> Vancouver elektrica Colocation and Data Centers 14 12-17-2009 03:06 AM
colocation in westin building in seattle jimmy Dedicated Hosting Offers 0 02-03-2005 03:05 AM

Related posts from TheWhir.com
Title Type Date Posted
Equinix Opens $60 Million Data Center in Seattle Web Hosting News 2013-03-15 16:35:14
PEER 1 and Tier 3 Extend Enterprise Cloud Offering into Canada Web Hosting News 2012-12-10 16:29:02
Amazon Explains Recent Cloud Outage was Caused by Power Failure Web Hosting News 2012-06-18 11:11:22
Colocation Provider Equinix to Build Third Data Center in Seattle Web Hosting News 2011-10-19 14:13:09
Data Center Power Failure Causes VoIP Service Provider Ooma Outage Web Hosting News 2011-08-18 15:22:21


Tags
bad design, data center, electrical, peer1, power loss

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes
Postbit Selector

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is Off
HTML code is Off

Forum Jump
Login:
Log in with your username and password
Username:
Password:



Forgot Password?
Advertisement:
Web Hosting News:



 

X

Welcome to WebHostingTalk.com

Create your username to jump into the discussion!

WebHostingTalk.com is the largest, most influentual web hosting community on the Internet. Join us by filling in the form below.


(4 digit year)

Already a member?