    TELEHOUSE 25 Broadway - POWER

    Dear valued customer,

    We extremely apologize for the unexpected power failure that was experienced to your equipment today. Telehouse has restored power to your equipments at this moment , currently our UPS vendor is investigating the cause of failure. If you still experience outage to any of your equipment please contact CAC at 718-355-2525 we will work with you to restore the power immediately. Also, CAC will be notifying the status update every two hours based on the vendor's diagnosis.

    Thank you so much for your cooperation and understanding.

    Regards,

    Partheepan "Raj" Rajaratnam
    TELEHOUSE America
    Assistant Manager
    Facilities Engineering & Operation

  2. #2
    Join Date
    Dec 2011
    Location
    Storrs, CT
    Posts
    64
    Really quite silly. UPS issue which caused a multi-hour outage. *sigh*

  3. #3
    Join Date
    Nov 2001
    Location
    New York / New Jersey
    Posts
    753
    Not the first time this has happened at 25 Broadway. Its been a few years though.

  4. #4
    Join Date
    Feb 2002
    Location
    New York, NY
    Posts
    4,618
    Ah, that brings back memories. I think they had 2 outages when we were there years ago. The second outage didn't affect us, because after the first, we had them run us a redundant circuit from another floor.

  5. #5
    Join Date
    Aug 2007
    Location
    L.A., CA
    Posts
    3,710
    Quote Originally Posted by djahandarie View Post
    Really quite silly. UPS issue which caused a multi-hour outage. *sigh*
    Quite silly? This stuff happens.

  6. #6
    Join Date
    Dec 2011
    Location
    Storrs, CT
    Posts
    64
    Quote Originally Posted by CGotzmann View Post
    Quite silly? This stuff happens.
    They lacked the redundancy, and/or the ability to bypass the UPS, and/or the ability to get the vendor/replacements on scene quickly. It does happen, but that doesn't mean I'm not going to complain about it .

  7. #7
    Join Date
    Feb 2002
    Location
    New York, NY
    Posts
    4,618
    Quote Originally Posted by CGotzmann View Post
    Quite silly? This stuff happens.
    When it happens every 2-3 years, it's a different story. It's my understanding that the outages we experienced there were not their first.

  8. #8
    Join Date
    Apr 2000
    Location
    Nevada, US
    Posts
    5,550
    Aren't they closing that facility soon?...I think so.
    .
    .

  9. #9
    Join Date
    Aug 2007
    Location
    Lincoln, UK
    Posts
    489
    Yeah, 25 Broadway is due to be shuttered in mid 2013 I think.

  10. #10
    Join Date
    Oct 2006
    Location
    New Jersey
    Posts
    110
    Here is update from TELEHOUSE as of 05/01/2012

    Dear Valued Customer,

    The following is a recap of activity and latest update on the power outage that
    occurred on Sunday, 4/29 affecting only UPS-A Customers at the TELEHOUSE 25 Broadway
    facility, in New York City.

    On Sunday evening at around 6PM, there was a commercial utility power drop. At that
    time, the primary UPS - A1 system failed to maintain critical power load apparently
    due to a fuse failure. The UPS A2 system, which is the failover or backup system to
    UPS A1, failed to carry the shifting load for undetermined reasons at this time. The
    diesel generators also failed to start again due to undetermined reasons at this
    time.
    Critical Power was restored using diesel generator at approximately 9:00PM Sunday
    and has been stable since that time.

    Current Status and Activities Timeline

    <4/30>
    - Our UPS vendor identified 2 failed (blown) inverter fuses and replaced all
    (6) the fuses on the UPS A1 inverter.
    - No failed (blown) fuses were identified in UPS A2.
    - UPS vendor swapped out the faulty inverter on UPS A1 and SCR tested new inverter
    for proper operation.
    - All the batteries on both units were load tested for voltage.

    <5/1>
    - Commercial utility power feeds are stable at this time.
    - Diesel generator power is stable.
    - Our UPS vendor performed the check on UPS#A2 this morning, and turned it on now
    with no-commercial load for testing.
    - Other proactive trouble shooting and testing is underway on UPS A systems.
    - All the load for UPS A system will be continue to be supported by generator system
    until UPS A is fully restored.
    - We are in the stage of finalizing the testing the power stability both for
    UPS-A1&2, and the transfer is scheduled to be done on May 3rd between the time frame
    (0000-0500) if we determine there is no problem to do so.

    Once the power is stabilized back to UPS-A1&2, further investigation into the root
    cause of this outage can be completed and documented for notice and any additional
    appropriate remedial action needed. TELEHOUSE remains committed at all times to
    providing you with up to date status on current conditions.

    Sincerely yours,

Similar Threads

  1. NYC - Telehouse 25 Broadway or Teleport Colocation
    By htbsales in forum Colo Hosting Offers
    Replies: 0
    Last Post: 08-01-2010, 11:36 PM
  2. NYC - Telehouse 25 Broadway Colocation. 1U for 79.95/monthly
    By htbsales in forum Colo Hosting Offers
    Replies: 0
    Last Post: 06-02-2010, 12:01 PM
  3. TELEHOUSE - 25 Broadway 1 Cabinet Left
    By lostpacket in forum Colo Hosting Offers
    Replies: 0
    Last Post: 03-07-2008, 12:28 PM
  4. Telehouse 25 Broadway waiting on Cabinets?
    By nero-x in forum Dedicated Server
    Replies: 3
    Last Post: 04-16-2004, 09:27 AM
  5. Additional Rackspace in Telehouse @ 25 Broadway
    By wlandman in forum Other Offers & Requests
    Replies: 0
    Last Post: 01-02-2003, 11:48 PM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •