What size server rack cabinet do I need? plz suggest
Hi,
Recently I am in market for 32U and 42U floor standing rack cabinet. But can't figure out what size should I go with for the servers in office.
Options I have is: 600x1000mm or 800x1000mm
which one to get?
All server we use are supermicro 818-14
http://www.supermicro.com/products/c...C818G-1400.cfm
from website dimension is
Width 17.2" (437mm)
Depth 28.2" (716mm)
I dont want to get in a situation that I brought one and later in office none of the servers fit.
plz suggest.TechWacky - The Social Tech Guide - HERE
(¯ Currently operate servers with: Wholesale Internet, EvoSwitch, DataShack
_) Previous servers: Limestone Networks, RapidSwitch, Poundhost, TailorMadeServers, JoesDC
-
06-03-2014, 07:36 AM #2Junior Guru Wannabe
- Join Date
- Apr 2013
- Location
- Ljubljana, Slovenia
- Posts
- 90
All servers are for 19" rack
If you have a chance use bigger rack as there will be more space for wiring
-
06-03-2014, 09:27 AM #3Rockin' the beer gut
- Join Date
- May 2006
- Location
- NJ, USA
- Posts
- 6,645
I always suggest deeper. As the poster above me said, more room for cabling and to work in the back there if you need to.
AS395558
-
06-03-2014, 10:55 AM #4WHT Addict
- Join Date
- May 2008
- Location
- DataCenter
- Posts
- 143
well the depth is 1000mm, which i believe is enough, as my server is just 716mm
I am confused with Width they say...600mm or 800mm <---what is that
I found this image..
http://docs.oracle.com/cd/E19088-01/...ackmount-8.gif
SO basically all server are 19" but when retailer say 600mm or 800mm width that means its saying the width of the cabinet from outside. is it?TechWacky - The Social Tech Guide - HERE
(¯ Currently operate servers with: Wholesale Internet, EvoSwitch, DataShack
_) Previous servers: Limestone Networks, RapidSwitch, Poundhost, TailorMadeServers, JoesDC
-
06-03-2014, 02:08 PM #5Web Hosting Master
- Join Date
- Jun 2003
- Location
- Los Angeles, CA
- Posts
- 1,686
Looks like a standard Supermicro 1U chassis, we usually get the APC AR-3100
Psychz Networks - Dedicated Servers, Co-location | PhotonVPS - SSD Cloud | YardVPS - Storage VPS
True Layer 7 DDoS Mitigation | BGP Optimized by Noction Intelligent Routing | Asia-Pacific Low Latency Routes
6 Continents - 14 Cities - LAX, DAL, CHI, ASH, LON, AMS, JNB, TPE, TKY, BOM, GRU, BCN, SIN, SYD, ICN, MOS
-
06-03-2014, 06:23 PM #6Web Hosting Master
- Join Date
- Aug 2007
- Location
- L.A., CA
- Posts
- 3,710
what cabinet are you looking at?? that would go a long way to tell you what the actual dimensions they are talking about are.
EasyDCIM.com - DataCenter Infrastructure Management - HELLO DEDICATED SERVER & COLO PROVIDERS! - Reach Me: chris@easydcim.com
Bandwidth Billing | Inventory & Asset Management | Server Control
Order Forms | Reboots | IPMI Control | IP Management | Reverse&Forward DNS | Rack Management
-
06-04-2014, 03:11 AM #7Web Hosting Guru
- Join Date
- Jun 2011
- Location
- Portsmouth, UK
- Posts
- 327
800mm is obviously the width, this gives you 100mm either side of the rack mounting frame which can be useful for cables passing cables from back to front (if you have limited rear access) etc.
Personally I don't think it'll help much, but it certainly won't do any harm to have one that's too big.
The number of U will control the height, 42U should go under most ceilings (44.45mm x 42U + feet & lid) normally ends up being about 2m.
When you're rack mounting make sure
1). You adjust your vertical posts correctly, personally I go as far forward as possible and then the back post wherever it fits in best with the hardware
2). You put your servers in actual U spaces, there are 3 holes in a U, the middle one whole of a U is further apart from the other two holes than the next U. If you don't use the correct holes you'll find servers don't fit
Re Depth, 1000mm is probably the minimum you want to consider, 800mm is possible but will be quite tight with most servers.
You should also consider the noise and heat, if you have 42 servers in an office it'll put out a few kW of heat and a few dB of noise and probably upset the neighbours. If you put it in a cupboard make sure it has some ventilation, servers like stable temps and nothing much about 27CServerHouse | Est 2001 | 3x UK Data centres | Roof access, satcoms | High density | DR as standard
http://www.serverhouse.co.uk
-
06-04-2014, 03:59 AM #8WHT Addict
- Join Date
- May 2008
- Location
- DataCenter
- Posts
- 143
Thanks a lot for the info. I don't need space for cable on side, as its going to be for 6 servers and one 24 port patch panel. I will go with 600x1000mm... 32U , front door is plexiglass. I will have easy access to rear. I will going with a brand called iview or inet. 32U will cost around 380ish USD.
TechWacky - The Social Tech Guide - HERE
(¯ Currently operate servers with: Wholesale Internet, EvoSwitch, DataShack
_) Previous servers: Limestone Networks, RapidSwitch, Poundhost, TailorMadeServers, JoesDC
-
06-04-2014, 04:13 AM #9Web Hosting Guru
- Join Date
- Jun 2011
- Location
- Portsmouth, UK
- Posts
- 327
Your servers suck cold air in the front and blow hot air out of the back.
Make sure your rack has vents to allow this, normally the more vents the better, with glass fronted racks you normally have vents at 45 degrees the glass, but you'll also need them at the back.
I wouldn't recommend putting fans in the top of the rack as this has been proven to only cool the top 1/4 of the rack.
Ideally we like to be able to feel the air blown from the servers out of the rack door when the door is closed, nice to know all the hot air is getting outServerHouse | Est 2001 | 3x UK Data centres | Roof access, satcoms | High density | DR as standard
http://www.serverhouse.co.uk
-
06-07-2014, 10:39 PM #10Junior Guru Wannabe
- Join Date
- Oct 2013
- Location
- Byfleet, Surrey, UK
- Posts
- 40
I agree,
Cold air flow is paramount within any size Rack especially the more equipment you are utilising within the rack.
Bad air flow can lead to premature server failure due to parts overheating and some parts generally becoming non functional i.e. HDD's, Fans, PSU's etc..4D Hosting - premium hosting solutions
VPS | Reseller Hosting | Exchange Email |
www.4dhosting.com |@4dhosting
-
06-08-2014, 07:56 PM #11Web Hosting Master
- Join Date
- May 2013
- Location
- USA
- Posts
- 931
▄▀▄ Brian Harrison, Lead Engineer - Reprise Hosting (AS62838)
▄▀▄ Deals on cheap dedicated server hosting. IPMI included! Unmetered bandwidth.
▄▀▄ Website migration, 24/7/365 support, basic server setup, 15 day money back.
▄▀▄ Looking for DEALS on self-managed cheap VPS hosting? Visit VPSHostingDEAL.com
-
06-09-2014, 03:05 PM #12Web Hosting Evangelist
- Join Date
- Nov 2012
- Location
- Los Angeles, CA
- Posts
- 499
Looks like one rack will do. it also depends on how much power these server may take. even though they are 1u servers it depends ob the processors and how much power they consume. so at the end of the day you may need one but for safe measure plan for two.
¦¦ COLOCATIONAMERICA.COM™ It’s All About Connections...™
¦¦ Colocation, Dedicated Servers, Premium Bandwidth, 24/7 Support!
¦¦ Los Angeles , New York , New Jersey , San Francisco , Chicago
¦¦ Email: Sales@ColocationAmerica.com for a quote or call 888-505-COLO!
-
06-11-2014, 06:49 AM #13WHT Addict
- Join Date
- May 2008
- Location
- DataCenter
- Posts
- 143
TechWacky - The Social Tech Guide - HERE
(¯ Currently operate servers with: Wholesale Internet, EvoSwitch, DataShack
_) Previous servers: Limestone Networks, RapidSwitch, Poundhost, TailorMadeServers, JoesDC
-
06-11-2014, 12:06 PM #14Web Hosting Master
- Join Date
- Aug 2007
- Location
- L.A., CA
- Posts
- 3,710
You didn't understand.
You should get mesh front AND rear. You have no use for the glass and it will just impede maximum intake airflow for cooling. You don't need the fans at the top though. Just make sure that when you rack equipment, you DO NOT leave spaces between equipment and any open gaps at the FRONT of the rack are closed off with blanking panels.
You do not want the hot exhaust air being recirculated thru the front of the servers from the gaps between equipment.EasyDCIM.com - DataCenter Infrastructure Management - HELLO DEDICATED SERVER & COLO PROVIDERS! - Reach Me: chris@easydcim.com
Bandwidth Billing | Inventory & Asset Management | Server Control
Order Forms | Reboots | IPMI Control | IP Management | Reverse&Forward DNS | Rack Management
-
06-11-2014, 01:34 PM #15WHT Addict
- Join Date
- May 2008
- Location
- DataCenter
- Posts
- 143
I know that I need mesh vented front door but because the server cabinet will be inside an office, due to the sound we are going with glass front. It is not an option but its must. regarding the cooling... aircon runs 24x7 inside office.
TechWacky - The Social Tech Guide - HERE
(¯ Currently operate servers with: Wholesale Internet, EvoSwitch, DataShack
_) Previous servers: Limestone Networks, RapidSwitch, Poundhost, TailorMadeServers, JoesDC
-
06-11-2014, 01:46 PM #16Web Hosting Master
- Join Date
- Aug 2007
- Location
- L.A., CA
- Posts
- 3,710
A lot of the noise will be from the rear as the air exhausts out
EasyDCIM.com - DataCenter Infrastructure Management - HELLO DEDICATED SERVER & COLO PROVIDERS! - Reach Me: chris@easydcim.com
Bandwidth Billing | Inventory & Asset Management | Server Control
Order Forms | Reboots | IPMI Control | IP Management | Reverse&Forward DNS | Rack Management
-
06-12-2014, 02:16 AM #17WHT Addict
- Join Date
- May 2008
- Location
- DataCenter
- Posts
- 143
I know.... that is everyone in office has to deal with.
TechWacky - The Social Tech Guide - HERE
(¯ Currently operate servers with: Wholesale Internet, EvoSwitch, DataShack
_) Previous servers: Limestone Networks, RapidSwitch, Poundhost, TailorMadeServers, JoesDC
Similar Threads
-
Quarter Cabinet, Half Cabinet, Full Cabinet and Single Server COLO _FIRST MONTH FREE_
By Dustin B Cisneros in forum Colo Hosting OffersReplies: 0Last Post: 06-02-2014, 01:20 AM -
Quarter Cabinet, Half Cabinet, Full Cabinet and Single Server COLO _FIRST MONTH FREE_
By Dustin B Cisneros in forum Colo Hosting OffersReplies: 0Last Post: 05-29-2014, 11:48 PM -
i want to buy dedicated server .Plz suggest
By scriptburnofficial in forum Dedicated ServerReplies: 20Last Post: 01-15-2011, 12:57 PM -
Server Rack size
By philman213 in forum Dedicated ServerReplies: 8Last Post: 05-18-2004, 10:44 PM -
WTB (today!) servers/systems. Rack, server or PC (case/size/type). What do you have?
By Tim Greer in forum Other Offers & RequestsReplies: 1Last Post: 03-30-2003, 10:10 PM