TELEHOUSE 25 Broadway - POWER


Dear valued customer,

We extremely apologize for the unexpected power failure that was experienced to your equipment today. Telehouse has restored power to your equipments at this moment , currently our UPS vendor is investigating the cause of failure. If you still experience outage to any of your equipment please contact CAC at 718-355-2525 we will work with you to restore the power immediately. Also, CAC will be notifying the status update every two hours based on the vendor's diagnosis.

Thank you so much for your cooperation and understanding.

Regards,

Partheepan "Raj" Rajaratnam
TELEHOUSE America
Assistant Manager
Facilities Engineering & Operation



Sponsored Links
  #2  
Old 04-29-2012, 11:50 PM
djahandarie djahandarie is offline
Junior Guru Wannabe
 
Join Date: Dec 2011
Location: Storrs, CT
Posts: 64
Really quite silly. UPS issue which caused a multi-hour outage. *sigh*

  #3  
Old 04-29-2012, 11:52 PM
lostpacket lostpacket is offline
Temporarily Suspended
 
Join Date: Nov 2001
Location: New York / New Jersey
Posts: 753
Not the first time this has happened at 25 Broadway. Its been a few years though.

Sponsored Links
  #4  
Old 04-30-2012, 02:50 AM
bqinternet bqinternet is offline
Backup Guru
 
Join Date: Feb 2002
Location: New York, NY
Posts: 4,470
Ah, that brings back memories. I think they had 2 outages when we were there years ago. The second outage didn't affect us, because after the first, we had them run us a redundant circuit from another floor.

  #5  
Old 04-30-2012, 02:48 PM
CGotzmann CGotzmann is offline
Privileged
 
Join Date: Aug 2007
Location: L.A., CA
Posts: 2,921
Quote:
Originally Posted by djahandarie View Post
Really quite silly. UPS issue which caused a multi-hour outage. *sigh*
Quite silly? This stuff happens.

  #6  
Old 04-30-2012, 02:52 PM
djahandarie djahandarie is offline
Junior Guru Wannabe
 
Join Date: Dec 2011
Location: Storrs, CT
Posts: 64
Quote:
Originally Posted by CGotzmann View Post
Quite silly? This stuff happens.
They lacked the redundancy, and/or the ability to bypass the UPS, and/or the ability to get the vendor/replacements on scene quickly. It does happen, but that doesn't mean I'm not going to complain about it .

  #7  
Old 04-30-2012, 03:12 PM
bqinternet bqinternet is offline
Backup Guru
 
Join Date: Feb 2002
Location: New York, NY
Posts: 4,470
Quote:
Originally Posted by CGotzmann View Post
Quite silly? This stuff happens.
When it happens every 2-3 years, it's a different story. It's my understanding that the outages we experienced there were not their first.

  #8  
Old 05-01-2012, 05:38 PM
HostJedi HostJedi is offline
Corporate Member
 
Join Date: Apr 2000
Posts: 5,140
Aren't they closing that facility soon?...I think so.
.
.

  #9  
Old 05-01-2012, 05:46 PM
freethought freethought is offline
Junior Guru Wannabe
 
Join Date: Aug 2007
Location: Lincoln, UK
Posts: 55
Yeah, 25 Broadway is due to be shuttered in mid 2013 I think.

  #10  
Old 05-01-2012, 08:29 PM
TadasPet TadasPet is online now
WHT Addict
 
Join Date: Oct 2006
Location: New Jersey
Posts: 110
Here is update from TELEHOUSE as of 05/01/2012

Quote:
Dear Valued Customer,

The following is a recap of activity and latest update on the power outage that
occurred on Sunday, 4/29 affecting only UPS-A Customers at the TELEHOUSE 25 Broadway
facility, in New York City.

On Sunday evening at around 6PM, there was a commercial utility power drop. At that
time, the primary UPS - A1 system failed to maintain critical power load apparently
due to a fuse failure. The UPS A2 system, which is the failover or backup system to
UPS A1, failed to carry the shifting load for undetermined reasons at this time. The
diesel generators also failed to start again due to undetermined reasons at this
time.
Critical Power was restored using diesel generator at approximately 9:00PM Sunday
and has been stable since that time.

Current Status and Activities Timeline

<4/30>
- Our UPS vendor identified 2 failed (blown) inverter fuses and replaced all
(6) the fuses on the UPS A1 inverter.
- No failed (blown) fuses were identified in UPS A2.
- UPS vendor swapped out the faulty inverter on UPS A1 and SCR tested new inverter
for proper operation.
- All the batteries on both units were load tested for voltage.

<5/1>
- Commercial utility power feeds are stable at this time.
- Diesel generator power is stable.
- Our UPS vendor performed the check on UPS#A2 this morning, and turned it on now
with no-commercial load for testing.
- Other proactive trouble shooting and testing is underway on UPS A systems.
- All the load for UPS A system will be continue to be supported by generator system
until UPS A is fully restored.
- We are in the stage of finalizing the testing the power stability both for
UPS-A1&2, and the transfer is scheduled to be done on May 3rd between the time frame
(0000-0500) if we determine there is no problem to do so.

Once the power is stabilized back to UPS-A1&2, further investigation into the root
cause of this outage can be completed and documented for notice and any additional
appropriate remedial action needed. TELEHOUSE remains committed at all times to
providing you with up to date status on current conditions.

Sincerely yours,

Reply

Similar Threads
Thread Thread Starter Forum Replies Last Post
NYC - Telehouse 25 Broadway or Teleport Colocation enotchnet Colo Hosting Offers 0 08-01-2010 11:36 PM
NYC - Telehouse 25 Broadway Colocation. 1U for 79.95/monthly enotchnet Colo Hosting Offers 0 06-02-2010 12:01 PM
TELEHOUSE - 25 Broadway 1 Cabinet Left lostpacket Colo Hosting Offers 0 03-07-2008 12:28 PM
Telehouse 25 Broadway waiting on Cabinets? nero-x Dedicated Server 3 04-16-2004 09:27 AM
Additional Rackspace in Telehouse @ 25 Broadway wlandman Other Offers & Requests 0 01-02-2003 11:48 PM

Related posts from TheWhir.com
Title Type Date Posted
KDDI Opens New Network Operations Center in Vietnam Web Hosting News 2013-08-15 11:53:53
Tsohost to Build 20,000 Square Foot Data Center in Slough Web Hosting News 2013-05-22 15:15:57
TELEHOUSE America Names New Chief Operating Officer Web Hosting News 2013-01-23 12:06:36
Colocation Firm Telehouse Expands Telehouse West Data Center in London Web Hosting News 2012-09-19 09:43:28
Telehouse Expands in Greater China with New Data Centers Web Hosting News 2012-06-11 10:49:09


Tags
telehouse

Thread Tools
Display Modes
Postbit Selector

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is Off
HTML code is Off

Forum Jump
Login:
Log in with your username and password
Username:
Password:



Forgot Password?
Advertisement:
Web Hosting News:



 

X

Welcome to WebHostingTalk.com

Create your username to jump into the discussion!

WebHostingTalk.com is the largest, most influentual web hosting community on the Internet. Join us by filling in the form below.


(4 digit year)

Already a member?